    Inverter compressor not pumpming



    Hello I have a Fujitsu Inverter compressor which I think is in efficient - haven't had this happen before - system runs at 16 degrees C at R410a suction temp/press, on closing liquid line took a long time to only reach 25 psi (175 kpa) suction pressure. Is this a proper test for an inverter style compressor? -has anyone encountered this before?
    any help appreciated



  2. #2
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Inverter compressor not pumpming

    Pls, specify a model name of unit.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Inverter compressor not pumpming

    should be able to pull a 10 inch vac, within 2 mins if the lp switch is linked out and the liq valve isnt passing

  4. #4
    Join Date
    Jul 2012
    Location
    Australia
    Age
    57
    Posts
    61
    Rep Power
    12

    Re: Inverter compressor not pumpming

    Thanks install monkey, do you generally replace inverter PC when replacing compressor?
    Hi bigor the mod no. is AOT45LJBYL
    Thank you

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Inverter compressor not pumpming

    check with fujitsu- some say as long as the 3 outputs are even, - then theres no need to replace it- as your compressor does start, then no need, if the compressor went down to earth or was siezing then your putting more strain on the inverter,
    http://www.mediafire.com/view/6696s1...ng%20Guide.pdf
    click on the link above for tayters guide for inverter checking- he also has a 24hr helpline as he can be found posting on here at 2am uk time!

    warranty can be limited to 6mths if inverter not changed with some manufacturers

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Inverter compressor not pumpming

    Not sure myself but would an inverter pump down on its own?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Inverter compressor not pumpming

    PUMP DOWN (Refrigerant collecting operation)
    Perform the following procedures to collect the refrigerant when moving
    the indoor unit or the outdoor unit.
    (1) Press the push-button switch on the circuit board once.
    The LED on the circuit board starts flashing (one second ON/one se-cond
    OFF). This indicates the start of PUMP DOWN operation.
    When the switch is pressed while the compressor is in operation, PUMP
    DOWN operation starts automatically.
    When the switch is pressed while the compressor is in stop, the com-pressor
    starts to operate automatically, and then move on to PUMP
    DOWN operation.
    (2) PUMP DOWN operation continues for about 1 minute. When PUMP
    DOWN operation is completed, the compressor stops automatically.
    Then close the 2-way valve and 3-way valve immediately.
    (3) Turn the power off.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Inverter compressor not pumpming

    http://www.mediafire.com/view/02xk31.../Manual(3).pdf
    similar service manual- click on link above- aota 30lbtl

  9. #9
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Inverter compressor not pumpming

    Sorry, I just to understand all this topic. You need to use advice of install monkey for compression test.
    And no good idea if you simple to close service valve then compressor is start.

  10. #10
    Join Date
    Jul 2012
    Location
    Australia
    Age
    57
    Posts
    61
    Rep Power
    12

    Re: Inverter compressor not pumpming

    Thanks for your advice, much appreciated.

  11. #11
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Inverter compressor not pumpming

    Bear in mind if you have the metal body fan motors they are reknowned for taking out PCB's left right and centre. If finances allow get the newer white plastic body motors.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Inverter compressor not pumpming

    Quote Originally Posted by Tayters View Post
    Bear in mind if you have the metal body fan motors they are reknowned for taking out PCB's left right and centre. If finances allow get the newer white plastic body motors.

    Cheers,
    Andy.
    Not really related to this thread methinks?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Inverter compressor not pumpming

    Not related to a non pumping compressor but related to the power surging through the unit when the isolator gets turned back on and a diode in the fan motor goes skew whiff and wrecks 2 other boards and you end up looking a bit of a plum.
    Health and safety first..........unless I'm in a hurry.

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Inverter compressor not pumpming

    is that tayters floggin them fujitsu fan motors again! by means of subliminal messages haha

  15. #15
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Inverter compressor not pumpming

    Quote Originally Posted by install monkey View Post
    is that tayters floggin them fujitsu fan motors again! by means of subliminal messages haha
    Ha, me kpi's need a boost!