Thread: R134a odour
    Dec 2008
    West Yorkshire
    63
    R134a odour
    Virgin R134a has an ethereal smell, however, I have noticed after a period of use in a system combined with POE oil there is a strong smell. Has anyone else encountered this and has anyone investigated the reason?
    Mar 2012
    italy
    67
    77
    13
    Re: R134a odour
    Check the value of acidity of the oil, can be the cause
    greetings
    May 2012
    59
    1,528
    36
    Re: R134a odour
    Refrigerants to me have no smell because I have a poor sense of smell
    (except for Ammonia ) so the only thing I smell is either the
    oil or the refrigerant that is thermally decomposed (burnt out).
    I do know that if 134a runs near to its critical point it will break down
    and then it smells burnt (if you lose some when fitting gauges).
    134a that is in a system with a blocked condenser or a faulty condenser
    fan often runs hotter than it's critical temperature (or near to it) and
    that often burns the refrigerant (thermally decompose). The only way
    to put it right is to replace the refrigerant for new (after cleaning the condenser).
    Smelly refrigerant is often put down to a burnt out compressor, but the refrigerant
    can break down if allowed to run too hot for too long.
    Rob
    Somerset
    69
    4,712
    Re: R134a odour
    Brilliant explanation Rob.
    Like you I have a poor sense of smell!
    So any unusual smells are investigated nowadays.
    Dec 2008
    West Yorkshire
    63
    Re: R134a odour
    Yes, I think it is due to the R134a breaking down too. It seems to happen quite a lot, but not with other refrigerants - unless, as you say, there is a problem with windings burning out or extreme heat.