Results 1 to 5 of 5

Thread: R134a odour

  1. #1
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    R134a odour



    Virgin R134a has an ethereal smell, however, I have noticed after a period of use in a system combined with POE oil there is a strong smell. Has anyone else encountered this and has anyone investigated the reason?



  2. #2
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: R134a odour

    Check the value of acidity of the oil, can be the cause

    greetings

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: R134a odour

    .

    Refrigerants to me have no smell because I have a poor sense of smell
    (except for Ammonia ) so the only thing I smell is either the
    oil or the refrigerant that is thermally decomposed (burnt out).

    I do know that if 134a runs near to its critical point it will break down
    and then it smells burnt (if you lose some when fitting gauges).
    134a that is in a system with a blocked condenser or a faulty condenser
    fan often runs hotter than it's critical temperature (or near to it) and
    that often burns the refrigerant (thermally decompose). The only way
    to put it right is to replace the refrigerant for new (after cleaning the condenser).

    Smelly refrigerant is often put down to a burnt out compressor, but the refrigerant
    can break down if allowed to run too hot for too long.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: R134a odour

    Brilliant explanation Rob.
    Like you I have a poor sense of smell!
    So any unusual smells are investigated nowadays.
    Grizzly

  5. #5
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    Re: R134a odour

    Yes, I think it is due to the R134a breaking down too. It seems to happen quite a lot, but not with other refrigerants - unless, as you say, there is a problem with windings burning out or extreme heat.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •