    o.d fan lock up on goodman, replaced works fine but::::



    i woke up the other morning and found my O.D fan was locked up on my goodman, i replaced no problems, my lights now blink, when compressor comes on. i let it heat up 24 hrs before turning unit back on. i haven't had time to check out my own unit been working too much. do you think compressor might have been hurt with no fan for 6 to 8 hrs. i haven't checked, by looks it wasn't bulged. i will have time monday to check out everthing, just wondering what others might think



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: o.d fan lock up on goodman, replaced works fine but::::

    Compressor may have been damaged running without an od fan, would think it would do less damage if the unit was in heating mode.

    Assuming you did not change the capacitor when you fitted the new motor, fitting a new dual run cap for the compressor and fan would be a good idea.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Aug 2010
    Location
    Southeast Penna.
    Age
    31
    Posts
    26
    Rep Power
    0

    Re: o.d fan lock up on goodman, replaced works fine but::::

    If it was running in heat mode without an outdoor (evaporator) fan, it probably flooded back and could have caused bearing or valve damage. Don't know how long it would have to run without a fan before causing permanent damage.

  4. #4
    Join Date
    Dec 2013
    Location
    us
    Age
    62
    Posts
    2
    Rep Power
    0

    Re: o.d fan lock up on goodman, replaced works fine but::::

    Quote Originally Posted by Jeremy Martin View Post
    If it was running in heat mode without an outdoor (evaporator) fan, it probably flooded back and could have caused bearing or valve damage. Don't know how long it would have to run without a fan before causing permanent damage.
    yeah, thats what i was afraid of i worked 14 today, that was the first thing i was going to do in morning , check caps and contactor, fan was 16 years old, unit was in good shape, i had took care of it.we had a ice storm the other day, my wife kept ice off of it, fan went out 2 days later. it seem to be working, proballly was about 6 to 8 hours,
    thanks for reply i will let you know