Toshiba vrf fault
Hi
Please could somebody help.
I had recently installed a Toshiba Vrf 3 pipe system about 3 months ago, all commissioned fine.
I returned to site earlier today and fitted remote return air sensors to each indoor void unit, when I switched the system back on I found fault E04 on the 1st 12 fan coils on the centralised controller, strange as these are not the first 12 from condenser but are 1 to 12 on the centralised.
I need to return to site tomorrow before the office workers return and being a sunday technical support is shut.
Do you think I need to do a master condenser reset, and also does anyone know the E04 error code.
Please help if you can
-
14-12-2013, 10:01 PM #2
Re: Toshiba vrf fault
e04 - comms error indoor-outdoor
http://www.mediafire.com/view/omlj0z...0Manual(2).pdf
click on link above for service manual
-
18-12-2013, 09:37 PM #3
Re: Toshiba vrf fault
E-o4 .one of the indoors has lost power.spur turned off