    Toshiba vrf fault



    Hi

    Please could somebody help.

    I had recently installed a Toshiba Vrf 3 pipe system about 3 months ago, all commissioned fine.

    I returned to site earlier today and fitted remote return air sensors to each indoor void unit, when I switched the system back on I found fault E04 on the 1st 12 fan coils on the centralised controller, strange as these are not the first 12 from condenser but are 1 to 12 on the centralised.

    I need to return to site tomorrow before the office workers return and being a sunday technical support is shut.

    Do you think I need to do a master condenser reset, and also does anyone know the E04 error code.

    Please help if you can



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba vrf fault

    e04 - comms error indoor-outdoor
    http://www.mediafire.com/view/omlj0z...0Manual(2).pdf
    click on link above for service manual

  3. #3
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Toshiba vrf fault

    E-o4 .one of the indoors has lost power.spur turned off