Results 1 to 29 of 29
  1. #1
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Flooded Ammonia Part Two



    The screw compressors are: Howden, Sullair, Mycom, and Dunham-Bush. Most of these are at least 20 years old, and all run very well.
    I'm qute familiar with Howden, Mycom and Dunham-Bush. Sullair I do not know at all. Proper maintenance and normal working conditions can keep them alive for a long time

    The one thing I do not like about the pumper drums is that you have to maintain a minimum gas pressure for pumping the liquid. Otherwise they are very simple to understand. You are exactly right about the NRV's.
    This one what we have here is working with condensing pressure. High pressure liquid cooler and pumper drum are in paralel connection do deliver a cold liquid to coolers. First we have liquid from pumper drum until is empty. Simultaneously we close the high pressure gas line to pumper drum and open equalizing gas line from pumper drum to surge drum to start gravity liquid filling into pumper drum. In the same time SV at cold liquid line from economiser is open to deliver cold liquid until pumper drum is full again and ready to deliver liquid. This is some kind of sequential work with about 3-5 minutes sequences for almost 30 years until now.

    This thread is getting very long. Perhaps we should start a new one??
    For that reason I started this one

    Yes, almost forget nothing about controls and valves: old one Phillips Refrigeration, Johnson Controls, Danfoss or other..



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Sullair started off by manufacturing twin screw compressors for compressed air systems. Sometime in the 1960's or 70's they started to package compressors for refrigeration applications; ammonia, *****, and helium among others.

    I installed several of these and really like them. Very simple, easy to work on...

    Sometime in the late 1980's they were involved in a very large heat pump system for an office building. R-22 liquid overfeed, ice banks for thermal storage, evaporative condensers, etc. An industrial refrigeration system being used for office air conditioning.

    Someone miscalculated the building envelope loads and the whole thing became a legal mess. Everyone had to pay some money. Shortly after that Sullair did not sell compressors for refrigeration service anymore.

    I don't know what the whole story was, but the legal problems left a bad feeling for everyone involved in the project from what I heard.

    The good thing about pumper drums is that you can change the transfer rate. A little more or a little less. It is hard to do that with a mechanically pumped system.

    I really prefer the mechanically pumped systems though. If you have the liquid feed valves setup properly, you can really reduce the discharge pressure on the compressors.

    If you reduce the discharge pressure on the pumper drums too much, the transfer rates begin to slow down so you could run out of liquid to the evaporators.

    If we can find enough to discuss, can we make it to "Flooded Ammonia, Part III?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Josip,

    Here is a picture of a Sullair screw compressor package.

    From one of my old catalogs...

    They were painted about the same color of green we have on the RE forum pages.
    Attached Files Attached Files

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by US Iceman
    Sullair.......... did not sell compressors for refrigeration service anymore.
    I don't know what the whole story was, but the legal problems left a bad feeling for everyone involved in the project from what I heard.
    Somebody did some mistake. The only way out was maybe to quit with refrigeration. Today they are famous for air service.

    The good thing about pumper drums is that you can change the transfer rate. A little more or a little less.
    It is hard to do that with a mechanically pumped system.
    I really prefer the mechanically pumped systems though. If you have the liquid feed valves setup properly, you can really reduce the discharge pressure on the compressors.
    If you reduce the discharge pressure on the pumper drums too much, the transfer rates begin to slow down so you could run out of liquid to the evaporators.
    Changing condensing pressure change the transfer rate too or you think on some other way.

    Using pumps is ok and very simple, having problem with pressure when you have a small cooling demand 2-3 roms out of 10-12.

    For that reason they install double ammonia charging lines to evaporators, one from pumper drum and another one from economiser coil. This coil is smaller becuse it is working during recharging of pumper drum.

    If we can find enough to discuss, can we make it to "Flooded Ammonia, Part III?
    Like Star Wars or The Lord of the Rings

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by US Iceman
    Josip,

    Here is a picture of a Sullair screw compressor package.

    From one of my old catalogs...

    They were painted about the same color of green we have on the RE forum pages.
    Very simple and very low almost at floor level. All of them in the begining were down.

    Today all of them are very high maybe for easier maintenance . You must have scaffolds around to do service.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by Josip
    Changing condensing pressure change the transfer rate too or you think on some other way?
    If your systems use the 3-way valve I think we can use a larger valve port. The larger valve port will allow more gas volume at the lower pressure differential.

    This is what I have seen.

    On one system we ran the discharge pressure down very low in the winter to see what would happen. Everything worked OK except for the pumper drums (these were for transfer, not liquid overfeed). The accumulator started to fill up because the transfer rate was not fast enough. The system shut down on high liquid level.

    I would expect a similar thing to happen on the liquid make-up valves (intercoolers, etc.). The lower pressure differential changes the valve capacity, so once again we need larger valve ports.

    The trick is to find a way to use multiple valves, or a valve that have sufficient capacity at both conditions (minimum and design differential).

    Using pumps is OK and very simple, having problem with pressure when you have a small cooling demand 2-3 rooms out of 10-12.
    What sort of problems do you have when only 2-3 rooms are cooling? Is it the pump discharge pressure or pump suction pressure?

    For that reason they install double ammonia charging lines to evaporators, one from pumper drum and another one from economiser coil. This coil is smaller because it is working during recharging of pumper drum.
    This sounds like you have only one pumper drum to feed the system. Most the systems I have seen will use two pumper drums. One fills, while the other is transferring liquid to the evaporators. After one has emptied, the other drum is ready to go. They cycle back and forth to maintain liquid supply.

    Can you provide a quick piping sketch of the system you describe please?

    Like Star Wars or The Lord of the Rings/
    A long time ago, in a place far, far away.... Someone started to use ammonia systems!

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by Josip
    Very simple and very low almost at floor level. All of them in the beginning were down
    I think the reason everyone started to mount the compressor and motor on the oil separators is that this saved a lot of cost. No structural steel and less welding.

    Some of the very large screws are still mounted down low. The separator shells cannot accommodate the very high weights and motor torque.

    Personally I like the lower models because they are much easier to work on. You do not have to be a monkey to work on anything.

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Flooded Ammonia Part Two

    If your systems use the 3-way valve I think we can use a larger valve port. The larger valve port will allow more gas volume at the lower pressure differential.
    This is what I have seen.
    Please can you send some piping scheme with 3-wy valves, picture can say more than thousand words Please, send some very typical and simple piping diagram
    This design is not comon here and I want to learn something more...

    On one system we ran the discharge pressure down very low in the winter to see what would happen. Everything worked OK except for the pumper drums (these were for transfer, not liquid overfeed). The accumulator started to fill up because the transfer rate was not fast enough. The system shut down on high liquid level.
    What about HG defrost if any, when you have very low condensing pressure? Can you, please, briefly explain idea to use pumper drums for liguid transfer to receiver. Is seems to me very complicated with so many level controls, valves... We do not use that system here and maybe I cann't see benefits.. I did see Phillips solutions (compressor protection) but still....

    What sort of problems do you have when only 2-3 rooms are cooling? Is it the pump discharge pressure or pump suction pressure?
    It is not too big problem, only higher discharge pressure. Another, sometimes bigger, problem is due to complete design and compressor capacity. For example for 10 cold rooms you choose proper compressor. Coming down to 2-3 rooms and running compressor even at minimum capacity you can come under set point causing pump stop due to low pressure difference (RT262). Pumps cycling and that is very bad, especially for hermetic pumps. Here I mean about industrial plants where client ask to install minimum units, but you know that story

    This sounds like you have only one pumper drum to feed the system. Most the systems I have seen will use two pumper drums. One fills, while the other is transferring liquid to the evaporators. After one has emptied, the other drum is ready to go. They cycle back and forth to maintain liquid supply.
    Can you provide a quick piping sketch of the system you describe please?
    This was designed by Stal Sweden to utilize eco port on compressor and for that reason we use one pumper drum and economiser. Yes I would like to send you piping sketc but unfortunately I have only one very bad blue print copy, from time when we use ozalid paper to copy drawings .

    Maybe I can make couple of scans and put them together to make it complete.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by Josip
    Please can you send some piping scheme with 3-way valves?
    Let me see what I can find today. I will post something if I can get the file size small enough.

    What about HG defrost if any, when you have very low condensing pressure?
    Over here we normally use pressure regulators (we call them defrost relief valves) to control the outlet coil pressure above a saturation temperature of 0C. Most of the time these valves are set for an equivalent saturation temperature of 10C.

    Since the defrosting pressure is set for the equivalent temperature of 10C, this establishes the minimum hot gas pressure you need. Now you have to add the pipe pressure losses to the defrost pressure setting of the valve.

    This total pressure is then the minimum pressure you need for the discharge pressure.

    I have worked on some systems where we were able to run the condensing temperature down to about 15C and still defrost the coils in under 30 minutes.

    Can you, please, briefly explain idea to use pumper drums for liquid transfer to receiver. Is seems to me very complicated with so many level controls, valves...
    There are many different types of these systems. When the transfer drums push the liquid to the high-pressure receiver, the transfer drums are normally located above the receiver. A little pressure difference and gravity allow the liquid to flow into the receiver.

    If the transfer drum pushes the liquid into a receiver controlled at a pressure lower than discharge pressure, you need sufficient differential to move the liquid.

    In other cases, a positive displacement pump is used to transfer the liquid. The Phillips compressor protection method is one way.

    As you say these are very complicated with all of the valves, small piping, controls, etc. I do not like these systems for those reasons. I prefer to keep things simple.

    Coming down to 2-3 rooms and running compressor even at minimum capacity you can come under set point causing pump stop due to low pressure difference...
    This sounds like pump cavitation due to decreasing compressor suction pressure from the large compressor size. The cooling loads are less than the compressor capacity, so when the suction pressure continues to decrease the pumps go into cavitation.

    In this case you need more capacity reduction in the system, but then you have already explained the problem.

    industrial plants where client ask to install minimum units...
    Since you have the Adobe software, can you draw a simple sketch of the piping on paper and then scan it into a PDF?
    Last edited by US Iceman; 10-03-2006 at 02:30 PM. Reason: correcting quote

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by Josip
    Please can you send some piping scheme with 3-way valves
    I did find one diagram for a single pumper drum system. The dual drum system is similar as far as I can remember.

    I hope this explains how the system is being used.

    Best Regards,
    US Iceman
    Attached Files Attached Files

  11. #11
    Join Date
    Jan 2002
    Location
    Long Beach Ca
    Age
    48
    Posts
    47
    Rep Power
    0

    Re: Flooded Ammonia Part Two

    hello everyone, put this link once before ,http://www.wea-site.com/papers.html makes for some good reading, well simplified. US Iceman ever work with any of the los angeles industrial people? my past company had a long relationship with mr Kohlenberger, just curious, best regards

  12. #12
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Flooded Ammonia Part Two

    Hello, US Iceman

    See attachments: freeeee
    acad zip and pdf, you can choose

    First start manually it was not nice. Not having a readable blue print drawing decide to make one in autocad. take some time but .....

    Some valves and lines missing but have no nervs to finish, hope it will be ok if not....ask

    Stan1488 your link seems pretty good, need some time to read it, thanks
    Attached Files Attached Files

  13. #13
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: Flooded Ammonia Part Two

    Hello

    just entered RE i just love ammonia iam form-Denmark home of Gram Danfoss and Sabroe, i have workede for Sabroe and Yorkref, i can see that you are a fan of sabroe Stan1488,

  14. #14
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Flooded Ammonia Part Two

    Welcome Casper,

    nice to have some more guys loving that stinking but natural fluid

  15. #15
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: Flooded Ammonia Part Two

    hey josip

    I just lookede at the system
    what is?

    The temp of the eco?
    the temp of the rooms?
    the pressof the eco?

  16. #16
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Hi guys,

    Welcome to the RE forum kasperDK. It is very nice to have other ammonia people to talk to.

    I'll try to answer some of the questions...

    Quote Originally Posted by stan1488
    ...ever work with any of the Los Angeles industrial people...?
    I know some people in sunny southern California. The name you mentioned sounds very familiar. When I used to work for a manufacturer I spent quite a lot of time with an ex-Frigid Coil person working on some air unit designs. I know the guys over at RETA National Headquarters in Salinas.

    Thank you for re-posting the web site link. I will review that also.

    Quote Originally Posted by Josip
    drawing...hope it will be OK if not....ask
    The drawing looks fine. I need to spend some time reviewing it.

    Quote Originally Posted by Josip
    nice to have some more guys loving that stinking but natural fluid
    I agree. The more people the better the discussion is.

  17. #17
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Hi Josip,

    Looked at your drawing.

    It looks like the high pressure gas for pumping liquid comes from the receiver. When the pumper drum is filling, the liquid from the economizer is flowing to the evaporators.

    After the pumper drum is full, the high pressure gas from the receiver pushes the liquid out of the drum and into the liquid line.

    One thing I have a question about is the liquid from the economiser. It is at discharge pressure. When the pumper drum transfers liquid into the liquid line is there a NRV in the liquid line from the economiser (before the liquid line from the pumper drum)?

    If the gas pressure to the pumper drum is lower than the liquid line pressure from the economiser, the liquid would not flow out of the pumper drum. Unless there is some elevation difference for gravity.

    Or, are there other control valves which help this?

    Perhaps I am missing something???

  18. #18
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: Flooded Ammonia Part Two

    i have the same idea but i think ther are a ON/OFF valve in the liquid line form the economiser ther are controled for the Pumper drum level indikator

    How dos this system react wenn you use HG defrost?

  19. #19
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: Flooded Ammonia Part Two

    Ther are a ON/off valve underthe suction return line to the seperator this must be controled form the level indikator in the Pumper drum

  20. #20
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by kasperDK
    i have the same idea but i think there are a ON/OFF valve in the liquid line form the economiser there are controlled for the Pumper drum level indicator
    That makes a lot of sense. When the pumper drum is ready to discharge liquid, the liquid line solenoid valve would close.

    The pressure in the liquid line would decrease due to the lower evaporating pressure. When the liquid line pressure is low enough, the liquid would then flow from the pumper drum.

    How dos this system react when you use HG defrost?
    That is a good question. I would like to hear from Josip about this.

  21. #21
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Now I see the valve. That completes the picture and answers the question.

  22. #22
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Flooded Ammonia Part Two

    Sorry guys,

    forget to put the marks on solenoids and NRV's

    On the liqid line before pumper drum is a flap type NRV (reason is; liquid by gravity force can open it to fill up pumper drum) after PD is normal check valve because we are using HP gas to push the liquid by opening left valve group on the top of PD. When we get the signal that PD is empty valve groups on the top of PD cycle (left OFF/right ON) to close the HP gas to equalize pressures in PD and surge drum and start gravity filling.

    Simultaneously with right valve group over PD we have ON signal to solenoid valve on liqiud line from economiser to evaporators. This liquid is some kind of make up (notice there is not other line for that) for complete system and liquid delivery during refilling of PD.

    There is not any HG defrost becuse this liquid enters machine for butter homogenisation. It is continuous process to produce butter and evaporating temp is -15C but for safety reasons (reduced production or something else) there is HG injection point to prevent freezing of butter and stuck of machinery. Each evaporator is eguipped with pressure and temperature controled valves becuse the quality of butter depends on process temperature.

    Complete valve stations for each evaporator (lot of different kind are installed there) were Danfoss. Process plant piping diagram I do not have but when I was there before 20+ years I was impressed and I asked about everything. Later on I was there couple of times for some services and use that time to study complete plant.
    Last edited by Josip; 11-03-2006 at 09:25 AM. Reason: correction of miswrite

  23. #23
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Josip,

    A very interesting system. Thank you for showing it to us.

    Best Regards,
    US Iceman
    Last edited by US Iceman; 11-03-2006 at 03:25 AM. Reason: spelling

  24. #24
    Join Date
    Dec 2005
    Location
    Norfolk, England
    Age
    66
    Posts
    132
    Rep Power
    19

    Re: Flooded Ammonia Part Two

    Hi. Ammonia Just love it, The best refrigeration liquid and gas you can use.

  25. #25
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Flooded Ammonia Part Two

    Hi Guys

    I recently designed a system for pumping all the ammonia charge out of a brine chiller on a cheese plant, prior to the tube side being cleaned by a CIP (Clean in place) system. I based my system on the Sabroe "Thermo Pump" used to cool oil in recip compressors.

    I thought I have designed something unique

    The process was as follows. using motorised valves.

    Shut off the liquid and pump out.
    Shut the suction off, evaporat pressure reg in circuit
    Open a drain valve at the bottom of the chiller to a drain vessel
    Pressure with hot gas, whilst opening a vent to the outlet side of the suction press reg

    Close drain valve on a low level cut out and stop the hot gas and start the CIP

    After CIP the chiller can be ran as normal with the hot gas used to push the liquid from the drain vessel to the main liquid line.

    It seems I have seen a drawing somewhere for a pumper system and copyied it without thinking

    Still I think pumper systems are a good idea

    Kind Regards. Andy.

  26. #26
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    I think the system Andy described is similar to some ice cream machines I have heard about. I can't remember the name, but I believe they German. Apologies to the company if I'm wrong.

  27. #27
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    8
    Rep Power
    0

    Re: Flooded Ammonia Part Two

    All I work on is Sullair Refrigeration products, if you have questions contact me at Mid-States Refrigeration.

  28. #28
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by Sullair Refrig View Post
    All I work on is Sullair Refrigeration products, if you have questions contact me at Mid-States Refrigeration.
    How are Jack and Tim doing? I have not talked to them for some time...
    If all else fails, ask for help.


  29. #29
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Flooded Ammonia Part Two

    Quote Originally Posted by Sullair Refrig View Post
    All I work on is Sullair Refrigeration products, if you have questions contact me at Mid-States Refrigeration.
    We get all our parts for the Sullairs through Mid-States. Welcome to RE

Similar Threads

  1. Want to be trained as an ammonia operator
    By Randy Williams in forum NH3
    Replies: 7
    Last Post: 26-11-2008, 08:15 PM
  2. part p
    By eggs in forum Electrical
    Replies: 25
    Last Post: 15-11-2007, 08:55 PM
  3. New Ammonia Certification in United States
    By JerrydNH3 in forum NH3
    Replies: 11
    Last Post: 15-08-2006, 03:10 PM
  4. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM
  5. Flooded Ammonia Refrigeration
    By stcornish in forum NH3
    Replies: 65
    Last Post: 17-03-2006, 03:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •