Results 1 to 19 of 19
Thread: carrier chiller
    Dec 2013
    IRAQ
    5
    Post carrier chiller
    [B]we have 3 carrier air cooled chiller we cant access to alarm icone
    who we can accses to this icone .this chiller has password levels
    can you help me
    Dec 2013
    IRAQ
    5
    Re: carrier chiller
    chiller model 30xa
    Jun 2009
    North East England
    41
    712
    Re: carrier chiller
    Password is 11
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Re: carrier chiller
    i think there is not two digit password. try it for alarm access 2222.
    Jun 2006
    South Coast
    278
    23
    Re: carrier chiller
    It depends on which type of display he has it is more likely to be 11 as he can't see the alarm menu.
    Oct 2007
    manchester
    5,639
    45
    Re: carrier chiller
    The default
    password is 0111. Use the arrow keys to change each number
    and press to accept the digit. Continue with the
    remaining digits of the password. The password can only be
    changed through CCN operator interface software such as
    ComfortWORKS®, ComfortVIEW™ and Service Tool
    Oct 2007
    manchester
    5,639
    45
    Re: carrier chiller
    Oct 2007
    manchester
    5,639
    45
    Re: carrier chiller
    i'll never get a job at carrier! haha
    FULL ACCESS PASSWORD — This configuration is used
    to specify the full access password. Refer to Table 1, Setup
    Menu, for additional information on passwords.
    Allowable Entries: 0 through 9999
    Default Value: 3333
    LIMITED ACCESS PANEL — This configuration is used to
    specify the limited access password.
    Default Value: 2222
    Jun 2006
    South Coast
    278
    23
    Re: carrier chiller
    Oh I don't know but could you afford the drop in wages IM.
    Jun 2006
    South Coast
    278
    23
    Re: carrier chiller
    French made XA's are either the Touch screen type password 2222 or Pro Dialog with buttons password is 11 enter enter.
    American XA using Comfortlink Touch Screen 2222.
    Sep 2005
    uk
    499
    21
    Re: carrier chiller
    Have you tried turning it off and on again.
    Takes a licking, keeps on ticking.
    Dec 2013
    IRAQ
    5
    Re: carrier chiller
    thanks for all
    i activated the password but the alarm( (control box thermostat))
    stall appear
    Dec 2013
    IRAQ
    5
    Re: carrier chiller
    sorry alarm is (electrical box thrmostat)
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    23
    Re: carrier chiller
    Electrical box interlock alarm is the safety for control box temperature. Check your panel ventilation, also I have seen some same chillers the wiring is series connected to external flow switch and chilled water pump interlock. Hence, if the flow switch is fail the same alarm will be displayed.
    Somerset
    69
    4,706
    Re: carrier chiller
    Quote Originally Posted by MANAF View Post
    An Electrical Box Thermostat Failure can also = Improper phasing detected by the reverse rotation board.
    Check- Check Power phasing, improper wiring or faulty rotation board.
    Logically yours is likely to be phasing of the power supplies?
    Good Luck Grizzly.
    Dec 2013
    IRAQ
    5
    Re: carrier chiller
    alsalam alykom
    thanks moideen for your last help .i have another proplem the touch screan not working and the chiller is runing .do you have spare part list for carreir chiller 30xa a or any carreir vender at our regon to make order to bay the spare parts. thank you again for your helps
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    23
    Re: carrier chiller
    alsalam alykom
    better to contact your carrier local dealer or you can purchase from Dubai through any courier service.
    Mar 2014
    Ghana
    4
    Re: carrier chiller
    Guys, I am new to this thread so pardon my mistakes. I have trane chillers (model ECGAL500) and trane air handling units to maintain but cant have access to the system because there is a password on it. Anyone knows how i can get it or reset it. Also any technical manual will be appreciated. Thanks guys!
  19. #19
    Jan 2014
    A, A
    2
    Re: carrier chiller
    plz tell me how to switch off a single circuit through the display.