    Discharge line bypass device utility ?



    Hi
    I checked a floor standing 4 ton LG split air conditioner unit
    there was a bypass valve connecting between the compressor discharge line
    and suction line
    the tube connect the valve from discharge line is larger than the capillary which connect the bypass valve to the compressor suction line

    these word are on the valve name plate
    SP 280 psi



    what its utility



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Discharge line bypass device utility ?

    Sounds like it is used for capacity control. It's either regulating or opening at 280psi.
    See Link: http://www.heatcraftrpd.com/res/pdfs...ty_Control.pdf (Page 8-9, Fig 2a)

    Another reason for piping a line to the suction would be for over pressure protection. Its not recommended here in Canada but still seen frequently.

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: Discharge line bypass device utility ?

    I took a photo for the valve from another unit
    bcoz the tag on the valve of the first unit was removed



  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Discharge line bypass device utility ?

    it's heat pump unit or not?

  5. #5
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: Discharge line bypass device utility ?

    its heat pump unit
    48000 btu

  6. #6
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Discharge line bypass device utility ?

    I had seen a similar circuit design in MHI units.
    Tomorrow I can upload mhi documents.

  7. #7
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: Discharge line bypass device utility ?

    Quote Originally Posted by bigor_2 View Post
    I had seen a similar circuit design in MHI units.
    Tomorrow I can upload mhi documents.
    im waiting

  8. #8
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Discharge line bypass device utility ?

    I think its like pre-error of HP. If compressor don't stop by currency/overheating with discharge->suction bypass, so let him work)))

  9. #9
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Discharge line bypass device utility ?

    kefah
    I'm sorry for my long silence.
    MHI's documents do not provide description of the work this valve.
    In some circuits he is called DPR
    DPR.png
    In other circuits he is called High Pressure regulator valve
    HPRV.png
    Look at it
    DPR1.jpg

    DPR2.jpg

    In both cases it is safety valve

  10. #10
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Discharge line bypass device utility ?

    First foto - Liquid injection and HP bypass ( after condenser to the suction)
    Second foto - HP drop, bypass capillary tubes.

    See that valve in old ME blocks r22