    Heat load calculation



    Hello :):):)

    Any one can help me to calculate the heat load of Compressed Air Dryer.

    Air Flow Rate is 100 CFM,
    Inlet Air Temperature is 45 dig C,
    Ambient Air Temperature is 40 dig C
    Air Pressure is 7 bar,
    Required Dew Point Temperature is 3 dig C.

    If u can pls teach me how to calculate it.
    Awaiting for your replay.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Heat load calculation

    Talk to an air compressor supplier, they supply driers as well.
    +3.0' C dew point is a big ask, may require several driers, and a pre-dehumidifier.
    Use a psychrometric chart, you will need the ambient wet bulb condition.
    No free engineering this week for first posters.

    magoo

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Heat load calculation

    Quote Originally Posted by Magoo View Post
    Talk to an air compressor supplier, they supply driers as well.
    +3.0' C dew point is a big ask, may require several driers, and a pre-dehumidifier.
    Use a psychrometric chart, you will need the ambient wet bulb condition.
    No free engineering this week for first posters.

    magoo
    Nice Magoo .... Like professor ....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •