    U4 error on Daikin fan unit model FTK25JVE 9
    Hello to everyone,
    Need your help guys on how to fix my a/c.
    Outdoor unit – RK35JVE 8
    Fan unit - FTK25JVE 9
    Symptom: Turn on, green lamp on fan coil blinking and louver does not open. I checked the condenser, it’s not working. Strangely, the a/c works in some days, but most of the time it doesn’t. I called a Daikin technician once, did some troubleshooting and all he said was replace the a/c since it’s already 10 years old. I don’t really believe him and I think he was just lazy to do further investigation.
    I’d like to try my luck at first before calling another technician or replacing the unit.
    Thank you.
    Oct 2007
    manchester
    5,639
    45
    Re: U4 error on Daikin fan unit model FTK25JVE 9
    had the same issue with a 5kw split- i installed 6yr earlier
    it states check the comms line (no 3) on the interconnecting cable- check your getting 150v ac pulsed signal- which i was- the conclusion was indoor pcb- 80 quid later, replaced pcb and same issue, tested interconnecting cable ok, turned out to be outdoor pcb, easiest way to check this- is turn the outdoor unit off at the isolator- wait a few mins, then power it up and listen for a faint whistling noise- note the green led on the outdoor sub pcb will flash as the indoor pcb, - so proove your cable is ok, if theres an indoor isolator/spur- check the wire on cable 3 isnt switched, check no rodents have nibbled at your cable, theres no condensate pump wired to 2 and 3 wire( should be 1 and 2)
    outdoor pcb was about 140 quid
    Oct 2001
    Nottingham UK
    5,667
    Your indoor and outdoor units are mis-matched