    pressure pump works but not the compressor



    Dear experts, I have a problem with my heat pump. the pressure pump works but not the compressor. Any ideas on why this is happening?

    thanks,



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    make of unit, model number, any flashing lights- what do you mean by pressure pump??

  3. #3
    Join Date
    Nov 2013
    Location
    Jordan
    Age
    48
    Posts
    16
    Rep Power
    0

    Re: pressure pump works but not the compressor

    Clivet WSAN EE121 .... the pump that circulates the water works ... the compressor though doesn't. All the flash lights start blinking in red.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    ah- hi iris- didnt recognise you , this clivet unit- how did you get on with running it in heating mode?

  5. #5
    Join Date
    Nov 2013
    Location
    Jordan
    Age
    48
    Posts
    16
    Rep Power
    0

    Re: pressure pump works but not the compressor

    Hi Steve .... we are still stuck. it doesn't switch to heating at all ... and although all the wiring is correct ... but the control pad doesn't seem to read any communication with the heat pump. We tried to start it up manually, but when we did.... the compressor failed and all flashes went on blinking on the pad. the only thing that works is the pump that circulates water.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    have you tried resetting it by holding the the "test" and "on/off" button for a few seconds
    see if it will run in cooling mode- (chances are by trying to run it in heating manually the controller has alarmed out)

  7. #7
    Join Date
    Nov 2013
    Location
    Jordan
    Age
    48
    Posts
    16
    Rep Power
    0

    Re: pressure pump works but not the compressor

    yes, we did.... the problem is the control pad doesn't respond at all .. even if you press and hold any button. The only one that works is the testing button...the one that shows whether all the connections are correct....

    when you connect the heat pump to the key pad ... the machine automatically starts on cooling (on its own) if you try to press on/off button for 20 seconds .... doesn't respond, the heating button ... no response.... what do you mean by the controller has alarmed out? can this be fixed and how?

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    try pressing the alarm button for about 30 seconds
    any fault code on the display E then 2 numbers or C and 2 numbers
    im trying to find wiring diagram and a pic of the pcb

  9. #9
    Join Date
    Nov 2013
    Location
    Jordan
    Age
    48
    Posts
    16
    Rep Power
    0

    Re: pressure pump works but not the compressor

    ok, i only have key pad (which is an indoor item) and the heat pump (the machine itself) ... is there anything else that is missing? the service keypad mentioned in the manual (the one that defines all the alarms and sets the parameters) ...this we dont have. this is why we are trying to operate it manually but the on/off buttons don't respond.

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    how far is the controller (indoor) to the chiller- im guessing its a 2 core screened cable-
    is the cable ok, no rodents nibbled at it, visual inspection of cable, any joints in the cable-
    is it run near mains cable, creating interference
    easiest way to check this if its a long cable run- is remove the controller and temporary wire it direct to the outdoor unit-
    Quote Originally Posted by ssaass View Post
    ok, i only have key pad (which is an indoor item) and the heat pump (the machine itself) ... is there anything else that is missing? the service keypad mentioned in the manual (the one that defines all the alarms and sets the parameters) ...this we dont have. this is why we are trying to operate it manually but the on/off buttons don't respond.

  11. #11
    Join Date
    Nov 2013
    Location
    Jordan
    Age
    48
    Posts
    16
    Rep Power
    0

    Re: pressure pump works but not the compressor

    we have moved the key pad next to the heat pump with a new cable (30 cms long). Some AC technicians came and said that it could be that the main module (the processor) of the machine has a production fault.. though I think it can't be, the machine is brand new and never run.

    Any other ideas?

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    put the controller back where it was originally fitted and get clivet out on a warranty claim

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: pressure pump works but not the compressor

    http://www.mediafire.com/view/e4x4l0...LL%20Norsk.pdf
    found this controller manual- unfortunatly its in german- goes in to more detail of the pcbs