    Green Oil
    Hi everyone, I have a 25kw mitsi electric (R410A) which had a compressor failure, I have replaced the pot but when I blew the pipework through with nitro the oil was green with a strange smell, don't know if this is some type of leak detector or acid clean up, has anyone seen this before ?,
    Regards,
    Skits.
    ireland
    54
    275
    26
    Re: Green Oil
    i have seen green oil after leak detecting dye was fitted to a plant . A uv light would tell you for certain if its dye or not.
    Somerset
    70
    4,700
    47
    Re: Green Oil
    Hi Skilts.
    Welcome to the forum!
    Joe-Ice is spot on where the green colour is very likely the type of dye (Oil) additive used to UV Leak check a fridge system.
    The smell given of from a motor burn out is highly pungent and may indeed be acidic?
    At minimum I would acid test your oil and seriously consider several oil changes and or filter changes at best!
    Grizzly.
    Aug 2009
    66
    31
    Re: Green Oil
    Hi and Thanks for the welcome,
    unfortunately the old pot was out of oil, so was unable to do an acid test,
    The pot is a fully hermetic so I,m unable to change the oil,
    The system has other problems, it has a very low back pressure causing high shell temp,
    I have cut out all the strainers in the condensor to no avail,
    I have had to isolate for now to avoid another failure,
    Skilts.
    11,024
    Re: Green Oil
    If the old pot was empty of oil then the oil is in the system somewhere.
    When the compressor starts it will eject a small percentage of oil. If there has been a problem with the system causing repeated starts then the compressor will end up without any oil in it which then completes the failure process.
    Your system now has double the design quantity of oil in it.
    Try blowing nitrogen through the system or you might need to run something like an Endoflush clean.
    Aug 2009
    66
    31
    Re: Green Oil
    I have only used Endoflush once & will never use it again, The suction line is 1 1/8 and horizontal, it will lay in any dip in the pipe & be impossible to remove from system as nitro will just sail over the top causing me a new problem.
    Skilts
    Oct 2007
    manchester
    5,639
    45
    Re: Green Oil
    see if oil has settled at thelowest point of the system- if its had glostick in it then theres issues with the quality of the installation- repipe or flush- pressure test the outdoor, and pipework individually to locate the leak
    Aug 2009
    66
    31
    Re: Green Oil
    The system does not have a leak on it although it may of had one in the past, I have a blockage of some type on the system that I cannot clear, I have removed 6 strainers from CU but still have very low back pressure, we are now considering replacing it, My concern is what is in the pipework & indoor units, Don,t want to wreck a new CU,
    Skilts
    Oct 2007
    manchester
    5,639
    45
    Re: Green Oil
    is it a power inverter
    Aug 2009
    66
    31
    Re: Green Oil
    Yh its a Mitsi Electric PUHZ-RP250YKA
    Oct 2007
    manchester
    5,639
    45
    Re: Green Oil
    was it installed with new pipework-
    or did they use "replacement technology" did they leave the carbon filter open to the circuit??
    Aug 2009
    66
    31
    Re: Green Oil
    Don't know as its a site we have taken over
    Oct 2007
    manchester
    5,639
    45
    Re: Green Oil
    has the pipework been modified to suit the condenser?
    does the pipework look as old as the condenser?
    usually if its original pipework theres a dip switch u flick to say the suction pipe is larger than required
    Oct 2012
    Russia
    42
    392
    Re: Green Oil
    http://yadi.sk/d/DGKzSd25DxhQm
    Oldschool Trane - compressor troubleshooting.
    52-52 page
    Aug 2009
    66
    31
    Re: Green Oil
    Yh very Good, Thanks for that
    Aug 2009
    66
    31
    Re: Green Oil
    Just an update, Mitsi have been to site to check on pressure problems, they told me to change LEV's , main PCB & triple vac system, however since that visit by their engineer, they have given us a new condenser, system is now working fine.