    Apr 2012
    Iraq
    35
    623
    Filter dryer installation vertically or horizontally ?
    hi every one
    as u know most of refrigerators come with filter dryer installed vertically
    once it been repaired bcoz of leakage or blockage etc...
    the technician here install the filter dryer horizontally
    they assume that if the filter dryer installed vertically that the contaminant will collect in the base of the filter and will lead to blockage of the system gradually by years
    is that correct
    Apr 2008
    Canada
    253
    4
    Re: Filter dryer installation vertically or horizontally ?
    Makes no difference.
    See attached for more information.
    http://sporlanonline.com/literature-...filter-driers/
    11,025
    On capillary line systems which connect direct with the drier they are mounted vertically to aid with the generation of a liquid seal at the start of the cap line.
    There is a coarse seive to hold back the filter material but if the filter starts breaking down then nothing much will stop the 'dust' from moving bthrough the system.
    Somerset
    69
    4,697
    Thanks Brian,
    As they say "You Learn something new Every Day!"
    Good question Kefah.
    Aug 2007
    Adelaide Australia
    70
    562
    Hi Kefah
    I was always taught to install the small copper driers as Brian has said vertically or at least at 45o with the outlet at the bottom. This would allow the drier to act like a small receiver so the capillary was always full of liquid.
    The problem with putting it in the horizontal is that if the system was charged by weight then it will probably be showing signs of being undercharged because there will be gas and liquid going to the evap instead of liquid only.
    Hope this helps
    Paul
    Born to fish, forced to work
    Apr 2012
    Iraq
    35
    623
    Grizzly[/QUOTE]
    thank u
    Apr 2012
    Iraq
    35
    623
    thank u
    man