    York Chiller programme failure - YAEP



    Hi,
    I have the following problem with the microprocessor board. Kindly advise if anybody has expertize about the york systems.

    The unit YAEP is not functioning as microprocessor board is found faulty due to 5V regulating supply is missing from it (tested at the TPs provided). So decided to change the board with a spare available(new board has come without eprom).

    After interchanging the Eprom & power-up, I find all the factory settings require reprogramming. for example starts with - Reprogram type of refrigerant to run
    when I try to enter through Keypad- 22 for R22, there is no response and also the same case with all other parameters.

    How I can reprogram the factory settings and what could be the problem? does it requires any code before entering?

    pl suggest, thanks in advance.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: York Chiller programme failure - YAEP

    use the arrow buttons to select gas

  3. #3
    Join Date
    Dec 2012
    Location
    Kuwait
    Age
    59
    Posts
    30
    Rep Power
    0

    Re: York Chiller programme failure - YAEP

    There are no such arrow keys provided on the keyboard. there is "+/-" key but not changing with it. I am attaching the image of keypad for understanding. anybody pl advise.
    Attached Files Attached Files