    panasonic U-4LA1E5



    Hi guys

    I had four wallmount units off the above outdoor unit with one wired controller. The wallmounts have now been fitted in seperate offices with there own controllers does anyone know if i need to re address the system and how this should be done if it needs done.I will be going back to site tomorrow to re comission the system,any help would be greatfull as i am not that familiar with panasonic.

    indoor models S-28KA1E5

    cheers gav



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: panasonic U-4LA1E5

    http://www.panasales.net.au/wp-conte...es_ServMan.pdf
    link to service manual- it says address the indoors manually would be better than auto address

  3. #3
    Join Date
    Sep 2010
    Location
    northern ireland
    Posts
    7
    Rep Power
    0

    Re: panasonic U-4LA1E5

    Thanks install monkey