    aspera compressor failure.



    Has anyone had a new compressor fail due to windings down to earth 10 minutes after start up.if so what did you find as the cause.just happened to me for the first time.the old compressor failed with the same problem.any ideas guys and gals.it is on a display counter.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: aspera compressor failure.

    hi doormaster ,
    tell me ,did you change the electric components on the unit?= sedgy

  3. #3
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: aspera compressor failure.

    Hi Sedgy. They came pre fitted. All we did was connect the mains.it was running perfectly.

  4. #4
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: aspera compressor failure.

    Check the contactor! I make it a habit to replace the contactor when replacing the compressor. Especially if the failure is electrical related.

    Do you have proper voltage?

  5. #5
    Join Date
    Dec 2013
    Location
    GB
    Age
    48
    Posts
    8
    Rep Power
    0

    Re: aspera compressor failure.

    It could be the capacitor. More than likely the start winding is staying in circuit.

  6. #6
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: aspera compressor failure.

    There is no contactor and voltage ok.compressor is only 1/2hp

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: aspera compressor failure.

    as long as input voltage is correct, you didnt dump liquid in it when it was running, correctly vacced, any crankcase heater energised then usually you dont have problems- also monitering operating pressures,running current whilst charging/comissioning.-any strange noises???
    but did you find the reason for the last pot failing- dirty coils, loose wire causing chattering, sometimes you can fit a duff pot- therefore- warranty

  8. #8
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: aspera compressor failure.

    Quote Originally Posted by install monkey View Post
    as long as input voltage is correct, you didnt dump liquid in it when it was running, correctly vacced, any crankcase heater energised then usually you dont have problems- also monitering operating pressures,running current whilst charging/comissioning.-any strange noises???
    but did you find the reason for the last pot failing- dirty coils, loose wire causing chattering, sometimes you can fit a duff pot- therefore- warranty
    Apparently the pipework in the condensate tray was replaced prior to the compressor failing

  9. #9
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: aspera compressor failure.

    doormaster,
    then theirs the answer then , there could be S H ONE TEE in the system , was there a new dryer fitted ?= sedgy

  10. #10
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: aspera compressor failure.

    Quote Originally Posted by sedgy View Post
    doormaster,
    then theirs the answer then , there could be S H ONE TEE in the system , was there a new dryer fitted ?= sedgy
    Hi sedgy.yes there was a new drier fitted.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: aspera compressor failure.

    was it vacced properly- did you weigh the charge in then run it?? or charge whilst running the pot?- sometimes the re evap trough is done in 5/16 pipe- so shisters use 1/4 pipe as its easier to bend- also was it a copper spun drier?? - clogged cappillary line
    if you didnt get the moisture/crap out the system, thats prob why pot went pop- remove duff pot, blow nitrogen down the suction line- with the open end ( discharge pipe) blow it for a good while- replace the drier for a flared 1 as you can get oxidation crap from brazing- this can also cause blockages