Thread: aspera compressor failure.
-
03-12-2013, 04:15 PM #1
aspera compressor failure.
Has anyone had a new compressor fail due to windings down to earth 10 minutes after start up.if so what did you find as the cause.just happened to me for the first time.the old compressor failed with the same problem.any ideas guys and gals.it is on a display counter.
-
03-12-2013, 05:15 PM #2
Re: aspera compressor failure.
hi doormaster ,
tell me ,did you change the electric components on the unit?= sedgy
-
03-12-2013, 06:24 PM #3
Re: aspera compressor failure.
Hi Sedgy. They came pre fitted. All we did was connect the mains.it was running perfectly.
-
Re: aspera compressor failure.
Check the contactor! I make it a habit to replace the contactor when replacing the compressor. Especially if the failure is electrical related.
Do you have proper voltage?
-
03-12-2013, 07:29 PM #5
Re: aspera compressor failure.
It could be the capacitor. More than likely the start winding is staying in circuit.
-
03-12-2013, 09:14 PM #6
Re: aspera compressor failure.
There is no contactor and voltage ok.compressor is only 1/2hp
-
03-12-2013, 09:20 PM #7
Re: aspera compressor failure.
as long as input voltage is correct, you didnt dump liquid in it when it was running, correctly vacced, any crankcase heater energised then usually you dont have problems- also monitering operating pressures,running current whilst charging/comissioning.-any strange noises???
but did you find the reason for the last pot failing- dirty coils, loose wire causing chattering, sometimes you can fit a duff pot- therefore- warranty
-
04-12-2013, 03:07 PM #8
-
04-12-2013, 03:17 PM #9
Re: aspera compressor failure.
doormaster,
then theirs the answer then , there could be S H ONE TEE in the system , was there a new dryer fitted ?= sedgy
-
04-12-2013, 09:13 PM #10
-
04-12-2013, 09:20 PM #11
Re: aspera compressor failure.
was it vacced properly- did you weigh the charge in then run it?? or charge whilst running the pot?- sometimes the re evap trough is done in 5/16 pipe- so shisters use 1/4 pipe as its easier to bend- also was it a copper spun drier?? - clogged cappillary line
if you didnt get the moisture/crap out the system, thats prob why pot went pop- remove duff pot, blow nitrogen down the suction line- with the open end ( discharge pipe) blow it for a good while- replace the drier for a flared 1 as you can get oxidation crap from brazing- this can also cause blockages