Results 1 to 5 of 5
Thread: carrier 30gx
-
02-12-2013, 07:54 PM #1
carrier 30gx
hi friends is there away to turn off 1 circuit on control panel to test run 1 circuit for a while.thankyou
-
02-12-2013, 08:20 PM #2
Re: carrier 30gx
4.5.6.3 - Manual tests
This function allows the user to test the outputs individually, if
the machine is completely shut down (LOFF). To carry out a
manual test use the arrow keys to access the output to be tested
and press the Enter key (longer than 2 seconds) to activate the
modification mode. The password is automatically requested, if
it has not previously been verified. The Outputs/Test LED on
the user interface begins to flash. Enter the desired test value
and again press Enter to start the test. 'TESt' is displayed on the
4-digit display alternately with the value tested. The Outputs/
Test LED stops flashing. Press the Enter key or an arrow key to
stop the test.
-
02-12-2013, 08:24 PM #3
Re: carrier 30gx
http://www.mediafire.com/view/p4saw1crqhqwsfz/13054.pdf
pro dialogue manual
possible access code
1111 Enter X4
courtesy of chillermans chiller password document
-
02-12-2013, 09:11 PM #4
Re: carrier 30gx
Just pull the plug off any one of the transducers on the circuit you don't want to run, it will go into alarm then you can run the circuit you want to run under test. When finished replace transducer plug and clear alarm.
Gibbo
-
02-12-2013, 09:59 PM #5
Re: carrier 30gx
Thankyou install and gibo