Results 1 to 15 of 15
Thread: Dakin vrv3
27-11-2013, 11:27 PM #1
Dakin vrv3
Just a quick one chaps. I have to decommission a daikin vrv3 system next week, need to remove all gas. Are the instructions for forcing open all the valves on the bs boxes in the outdoor unit and easy to understand? If not, can somebody give some pointers on how to do it? I don't know the model number but i do know it is only a couple of years old.
Andy
28-11-2013, 04:25 PM #2
28-11-2013, 07:08 PM #3
Re: Dakin vrv3
hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job
28-11-2013, 10:37 PM #4
28-11-2013, 11:14 PM #5
Re: Dakin vrv3
Ta very much chaps.
On the subject of schrader core depressors, do not attempt to change a lp pressure transducer on a MHI with the gas in - they don't have schraders
29-11-2013, 06:54 PM #6
Re: Dakin vrv3
Setting 21 .. On outdoor pcb main , hold mode button for around 5/6 seconds untill it gos solid then press set button 21 times , then return button once hp7 will flash , press set once , 6 will flash , then return twice , leaving only mode 1 solid , this is now in refrigerant recovery mode
29-11-2013, 06:56 PM #7
Re: Dakin vrv3
I thought most 410a were brazed switches / transducers
30-11-2013, 04:37 PM #8
30-11-2013, 04:38 PM #9
30-11-2013, 06:27 PM #10
30-11-2013, 07:04 PM #11
Re: Dakin vrv3
Degas from ports liquid\gas, didnt see any problems. 21 no need.
30-11-2013, 07:34 PM #12
30-11-2013, 10:21 PM #13
Re: Dakin vrv3
Always better to put setting 21 in for recovering , pressure testing and charging
30-11-2013, 10:24 PM #14
Re: Dakin vrv3
When doing it on 407 systems indoors to be turned off first
01-12-2013, 06:04 PM #15
Re: Dakin vrv3
If you system have BP units - 21 need, if no - just evacuate