    Dakin vrv3



    Just a quick one chaps. I have to decommission a daikin vrv3 system next week, need to remove all gas. Are the instructions for forcing open all the valves on the bs boxes in the outdoor unit and easy to understand? If not, can somebody give some pointers on how to do it? I don't know the model number but i do know it is only a couple of years old.

    Cheers

    Andy



  2. #2
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: Dakin vrv3

    Quote Originally Posted by Andy AC View Post
    Just a quick one chaps. I have to decommission a daikin vrv3 system next week, need to remove all gas. Are the instructions for forcing open all the valves on the bs boxes in the outdoor unit and easy to understand? If not, can somebody give some pointers on how to do it? I don't know the model number but i do know it is only a couple of years old.

    Cheers

    Andy
    Yep on the electric cover on the right hand side working on one currently changeling a lp sensor

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Dakin vrv3

    hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job

  4. #4
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: Dakin vrv3

    Quote Originally Posted by install monkey View Post
    hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job
    Trying to save the polar bears

  5. #5
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Dakin vrv3

    Ta very much chaps.
    On the subject of schrader core depressors, do not attempt to change a lp pressure transducer on a MHI with the gas in - they don't have schraders

  6. #6
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Dakin vrv3

    Setting 21 .. On outdoor pcb main , hold mode button for around 5/6 seconds untill it gos solid then press set button 21 times , then return button once hp7 will flash , press set once , 6 will flash , then return twice , leaving only mode 1 solid , this is now in refrigerant recovery mode

  7. #7
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Dakin vrv3

    I thought most 410a were brazed switches / transducers

  8. #8
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Dakin vrv3

    Quote Originally Posted by install monkey View Post
    hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job
    VRV III - You have to de-gas to change l/p transducer.

  9. #9
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Dakin vrv3

    Quote Originally Posted by Darrenp View Post
    Setting 21 .. On outdoor pcb main , hold mode button for around 5/6 seconds untill it gos solid then press set button 21 times , then return button once hp7 will flash , press set once , 6 will flash , then return twice , leaving only mode 1 solid , this is now in refrigerant recovery mode
    Ditto this

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Dakin vrv3

    thought u were on a daikin- glad u didnt snatch it
    Quote Originally Posted by AbsoluteWDJ View Post
    VRV III - You have to de-gas to change l/p transducer.

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Dakin vrv3

    Degas from ports liquid\gas, didnt see any problems. 21 no need.

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Dakin vrv3

    Quote Originally Posted by RusBuka View Post
    Degas from ports liquid\gas, didnt see any problems. 21 no need.
    still some gas pockets if done that way.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Dakin vrv3

    Always better to put setting 21 in for recovering , pressure testing and charging

  14. #14
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Dakin vrv3

    When doing it on 407 systems indoors to be turned off first

  15. #15
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Dakin vrv3

    If you system have BP units - 21 need, if no - just evacuate