Thread: Advice required
08-03-2006, 08:07 AM #1
Advice required
- we have ALCO expansion valve TCLE 7.5 FW (7.5 tons for R-12), can we use it on R-22 beacuse we recently used R-22 valves for R-407C by adjusting the superheat
- What is change in composition of suction and liquid filter drier, can we use suction drier in liquid line with capacity deration?
- Copeland agrees that we can change R-22 to R-407C(compressor) by change of POE oil for semi hermetic, why is it so i m bemused coz y then are they using 2 different models for R-22 and R-407C
Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
01-10-2006, 02:04 PM #2
Re: Advice required
Your TCLE 7.5 FW cannot be used for R22/R407C application because the bulb charge is intended only for R12 use and it is oversize for R22/R407C application and may result to low superheat and liquid slugging.
Liq line filter/drier has a higher %age of moisture removal. You may use STAS or ADKS for liq/suction line
Mineral oil is not compatible with R407CLast edited by Peter_1; 02-10-2006 at 02:12 PM. Reason: wrong typing
01-10-2006, 03:11 PM #3
Re: Advice required
They WERE using two different models. Now they are using POE also for R22 applications. You can't use mineral for R407c though.
01-10-2006, 03:26 PM #4
Re: Advice required
Copeland is quite right in suggesting that by changing the oil POE you can use the R22 semihermetic compressor to R 407c. Mineral oil is not misissible with R 407c. As for the Expansion Valve it is a different issue and the same has been very nicely and clearly stated by the above two posts.
Advice Needed!
By Tim_Uk_Trainee in forum TrainingReplies: 4Last Post: 05-06-2005, 11:01 PM -
planning to work in spain advice required
By frosty74 in forum Chit Chat & Service StoriesReplies: 24Last Post: 13-05-2005, 09:22 PM -
Advice for newbie - please be kind..!
By electricstuff in forum Air ConditioningReplies: 11Last Post: 04-10-2004, 06:52 PM -
Good advice!
By shogun7 in forum Chit Chat & Service StoriesReplies: 0Last Post: 03-09-2004, 01:06 AM