Thread: Advice required
    Apr 2004
    Pakistan
    44
    129
    Advice required
    • we have ALCO expansion valve TCLE 7.5 FW (7.5 tons for R-12), can we use it on R-22 beacuse we recently used R-22 valves for R-407C by adjusting the superheat
    • What is change in composition of suction and liquid filter drier, can we use suction drier in liquid line with capacity deration?
    • Copeland agrees that we can change R-22 to R-407C(compressor) by change of POE oil for semi hermetic, why is it so i m bemused coz y then are they using 2 different models for R-22 and R-407C
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
    Sep 2006
    Manila
    12
    Re: Advice required
    Your TCLE 7.5 FW cannot be used for R22/R407C application because the bulb charge is intended only for R12 use and it is oversize for R22/R407C application and may result to low superheat and liquid slugging.
    Liq line filter/drier has a higher %age of moisture removal. You may use STAS or ADKS for liq/suction line
    Mineral oil is not compatible with R407C
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Advice required
    They WERE using two different models. Now they are using POE also for R22 applications. You can't use mineral for R407c though.
    May 2006
    India
    82
    1,013
    Re: Advice required
    Copeland is quite right in suggesting that by changing the oil POE you can use the R22 semihermetic compressor to R 407c. Mineral oil is not misissible with R 407c. As for the Expansion Valve it is a different issue and the same has been very nicely and clearly stated by the above two posts.
  1. Advice Needed!
    By Tim_Uk_Trainee in forum Training
    Last Post: 05-06-2005, 11:01 PM
  2. planning to work in spain advice required
    By frosty74 in forum Chit Chat & Service Stories
    Last Post: 13-05-2005, 09:22 PM
  3. Advice for newbie - please be kind..!
    By electricstuff in forum Air Conditioning
    Last Post: 04-10-2004, 06:52 PM
  4. Good advice!
    By shogun7 in forum Chit Chat & Service Stories
    Last Post: 03-09-2004, 01:06 AM