    mitsi heavy centralised controller issues



    greetings
    customer has a vrf system with no local remote controllers-1 centralised scsl3na-ae
    approx 18mth old- software version 3.10e
    checked the time schedules and all the kit has to start up at 1am as the building fabric is poor- high ceiling void- uninsulated ceiling tiles
    monday,tues morning- staff say controller locks up- touching the screen doesnt light up- they have to remove the front cover and reset it on the rocker switch- im going to site again tomorrow at 7am to hopefully see this
    ive checked connections on the back of controller,comms ok

    previously when this happened they installed a ups to ensure power to the controller as they think it could be mains incoming issues- media city is 300yrds away so probably the bbc zapping al the leccy
    when it resets the time/date is correct- it times out for 240 secs whilst it reboots
    feel free to suggest
    oh and no fault codes stored- all works ok once rebooted
    ps i didnt fit it
    Last edited by install monkey; 26-11-2013 at 07:28 PM. Reason: additional info



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsi heavy centralised controller issues

    found operation manual states it could be electrostatic discharge- would wrapping the power supply 3 times around a ferrite core fix this?

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsi heavy centralised controller issues

    Typical- on site all working!

  4. #4
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: mitsi heavy centralised controller issues

    Whats the system? All indoor and outdoor units same series? SL1 or SL2?
    The controller may overheat due to the lack of air circulation.
    Last edited by RusBuka; 27-11-2013 at 10:44 AM.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsi heavy centralised controller issues

    hi ruskbuka - controller is in a plastic enclosure- it is warm inside- but not toasty
    all indoors are same series- think its a kx4 outdoor- comms line isnt grounded at the controller has run all day ok, suspect the comms line and the mains flex in the wall is causing problem- if it comes in again then ill run the comms externally to see if that cures it