    High condenser sub cooling



    Hi,
    I have a problem with the condenser running for 134system dryer unit. It was punctured beyond repairs due to unknown problem. so I have installed a non standard condenser unit meant for r22 as i do not have a similar one. It was placed away from the original position and on ground level (original condenser was at 3feet height).
    On starting the unit, we find compressor was running with high pressure and sub cooling is also very high about 25-30k. what could be the reason for this High pressure?

    will the distance and reduction in height affect the Hp? If i can bring down the hp i can solve the other problems.
    134a system

    hp-225psi
    condensing temp- 24c
    inlet air temp-23-24c
    outlet air - 29-30



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: High condenser sub cooling

    Is the condenser piped correctly?
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: High condenser sub cooling

    Over charged????



  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: High condenser sub cooling

    Is the new condensing unit the correct size?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2012
    Location
    Kuwait
    Age
    58
    Posts
    30
    Rep Power
    0

    Re: High condenser sub cooling

    Condenser is not overcharged for sure. infact charge is inadequate.
    Condenser is not originally designed for air dryer application. It was designed for R22 air handling system and constructionally is different in shape . its capacity size is more or less same and pipe size looks to be same.

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: High condenser sub cooling

    You have air in the system.
    Remove refrigerant , vacuum to 500micron or below, recharge with new refrigerant.

  7. #7
    Join Date
    Dec 2012
    Location
    Kuwait
    Age
    58
    Posts
    30
    Rep Power
    0

    Re: High condenser sub cooling

    i would like to know whether any modification is required. i mean
    1. its increased distance from compressor will create any resistance?
    2. original condenser was placed at a height above the liquid accumulator. now the present condenser piping is below the accumulator level. will this lift in piping create more resistance for flow and cause pressure to increase?

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: High condenser sub cooling

    Quote Originally Posted by tvrao View Post
    i would like to know whether any modification is required. i mean
    1. its increased distance from compressor will create any resistance?
    2. original condenser was placed at a height above the liquid accumulator. now the present condenser piping is below the accumulator level. will this lift in piping create more resistance for flow and cause pressure to increase?
    You are clutching at straws here, this is not your problem.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: High condenser sub cooling

    Quote Originally Posted by mad fridgie View Post
    You have air in the system.
    Remove refrigerant , vacuum to 500micron or below, recharge with new refrigerant.

    I agree with Mad Fridgie. Sounds like non-condensables!

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: High condenser sub cooling

    Check system for non- condensible gases by stooping it, isolate compressor, turn on condenser fan and after 10 minutes of fan working, measure air entering temperature and pressure in condenser. If you have any difference from PT chart for used refrigerant you have non-condensibile gases.

    After that check is done, and you find that non condensible gases are not problem here, then you probably have situation where liquid is backing up in condenser. It could be because of liquid receiver placement, but not necessary because of that. Any restriction in line from condenser to TXV can be possible reason and therefore you need to check everything by accurate temperature measurement of liquid pipes before and after each component on that line.
    Last edited by nike123; 08-12-2013 at 08:38 AM.

  11. #11
    Join Date
    Dec 2012
    Location
    Kuwait
    Age
    58
    Posts
    30
    Rep Power
    0

    Re: High condenser sub cooling

    Hi everyone. Thanks and Let me share my experience with this problem which is sorted out now. As many of you have expected, I found the air in the refrigerant system. The evaporator coil was leaking inside and entered into the LP side of the circuit. It has resulted continues increase in HP and unit was tripping.

    Regards