Results 1 to 21 of 21
  1. #1
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    fujitsu inverter problem



    hello my friends!
    I face some problems with a fujitsu inverter a/c.

    model: asya 12 lcc

    indoor (on the mask) indicator leds:

    red green
    flashing flashing (together)
    flashing flashing (together)
    flashing
    flashing
    flashing
    flashing
    .........................................

    even in fan mode the a/c is not functioning.
    can you help with some information and service manual?
    thanks in advance!



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: fujitsu inverter problem

    http://www.mediafire.com/view/3ds6pd...9/ASYA12LC.pdf
    check the speed of the flashes - service manual above

  3. #3
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    indoor fan motor is blocked. with a high probability will need to replace the motor.

  4. #4
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Firstly thanks for the manual,
    Secondly the error described in the manual is "locked indoor fan".
    What is the reason for this error?
    The fan or the circuit border?

  5. #5
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Sorry, the error is "abnormal lock" of the indoor fan.

  6. #6
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    error fan motor.png
    check +15vdc on connector CN2 (fan motor).

  7. #7
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Thanks.I amgoing to check it and then I will inform the rest of the team.

  8. #8
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    This motors is not survive after hot disconnect/connect. Remember it!

  9. #9
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    What are you meaning "hot".

  10. #10
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    HOT if power supply is ON.

  11. #11
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    The cn2 has 5 coloured cables.
    Which of them should I take the dcvolt?

  12. #12
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    fan motor.png
    Black and white.

  13. #13
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Thanks my friend for the quick answer.

  14. #14
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    The dc fan motor accept the 15 dc volt but it should emit a voltage~signal towardsthe circuit so ad to the latter realise that the fan is working well.Am i right?

  15. #15
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    If 15vdc (between black and white wire) and check 300vdc (between black and red wire) is present that motor is broken.

  16. #16
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Where can i find the schematic diagram of the fan motor?

  17. #17
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    Do you want it to disassemble and fix it?

  18. #18
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    I want to measure the windings of the fan

  19. #19
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: fujitsu inverter problem

    It is dc motor. Can not ping the coil because between connector and windings there is IC driver.

  20. #20
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Can you give me a photo or example of what you are reffering to ?

  21. #21
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •