Results 1 to 21 of 21
Thread: fujitsu inverter problem
24-11-2013, 03:19 PM #1
hello my friends!
I face some problems with a fujitsu inverter a/c.
model: asya 12 lcc
indoor (on the mask) indicator leds:
red green
flashing flashing (together)
flashing
flashing
flashing
flashing
even in fan mode the a/c is not functioning.
can you help with some information and service manual?
thanks in advance!
24-11-2013, 03:23 PM #2
Re: fujitsu inverter problem
http://www.mediafire.com/view/3ds6pd...9/ASYA12LC.pdf
check the speed of the flashes - service manual above
24-11-2013, 08:11 PM #3
indoor fan motor is blocked. with a high probability will need to replace the motor.
24-11-2013, 08:32 PM #4
Firstly thanks for the manual,
Secondly the error described in the manual is "locked indoor fan".
What is the reason for this error?
The fan or the circuit border?
24-11-2013, 08:34 PM #5
Sorry, the error is "abnormal lock" of the indoor fan.
25-11-2013, 06:32 AM #6
check +15vdc on connector CN2 (fan motor).
25-11-2013, 09:26 AM #7
Thanks.I amgoing to check it and then I will inform the rest of the team.
25-11-2013, 09:38 AM #8
This motors is not survive after hot disconnect/connect. Remember it!
25-11-2013, 09:59 AM #9
What are you meaning "hot".
25-11-2013, 10:17 AM #10
HOT if power supply is ON.
25-11-2013, 11:16 AM #11
The cn2 has 5 coloured cables.
Which of them should I take the dcvolt?
25-11-2013, 11:22 AM #12
Black and white.
25-11-2013, 11:29 AM #13
Thanks my friend for the quick answer.
25-11-2013, 11:44 AM #14
The dc fan motor accept the 15 dc volt but it should emit a voltage~signal towardsthe circuit so ad to the latter realise that the fan is working well.Am i right?
25-11-2013, 12:23 PM #15
If 15vdc (between black and white wire) and check 300vdc (between black and red wire) is present that motor is broken.
26-11-2013, 06:32 AM #16
Where can i find the schematic diagram of the fan motor?
26-11-2013, 06:37 AM #17
Do you want it to disassemble and fix it?
26-11-2013, 06:40 AM #18
I want to measure the windings of the fan
26-11-2013, 06:54 AM #19
It is dc motor. Can not ping the coil because between connector and windings there is IC driver.
26-11-2013, 07:20 AM #20
Can you give me a photo or example of what you are reffering to ?
26-11-2013, 07:42 AM #21