    Hi There new to a/c been a engineer now for abput 1 year



    Hi there i have a Fujitsui wall mounted a/c splt model number AOYR09LGC condenser. This is very strange what happens, put the gauges on the l/p side and they read 10 bar turn unit on and no fault codes come up and pressures dont change, but when i take my gauges off and some r410a is realised into the air the compressor some times kicks in and the unit runs fine ??????? until it goes into defrost or reaches temp. it will only start if i take my gauges of again



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hi There new to a/c been a engineer now for abput 1 year

    if the gauge lines are new then they can sometimes partially depress the schraeder core
    when u start the unit- run it in test mode on the controller- there can be a 3min delay- check the outdoor unit for loose connections
    click on link below to view service manual
    http://www.manualslib.com/manual/452...?page=5#manual

  3. #3
    Join Date
    Nov 2013
    Location
    england
    Age
    44
    Posts
    2
    Rep Power
    0

    Re: Hi There new to a/c been a engineer now for abput 1 year

    ok will check for lose connections also run in test mode and nothing happend with the gauges they stayed at 10bar. thanks for the reply and manual. i thought it might be the capacitor not holding a charge but by the looks at the drawing theres not one strange