Thread: Climaveneta Chiller problem
-
21-11-2013, 03:07 PM #1
Climaveneta Chiller problem
Hi frens...
we had installed two Climaveneta chillers on the Hospital, Model number: NECS-N/D/B 2818 and the S/NO:32023515
the problems found on the chillers are as follows:-
Chiller No. 1
Compressor of circuit trips with in a minute and shows Compressor fault error..
CHILLER NO- 2
Compressor of circuit trips with in a minute and shows Compressor fault error.
what will be the main reason behind it and waiting for the prompt reply..!!
Cheers...
-
21-11-2013, 06:05 PM #2
-
21-11-2013, 06:16 PM #3
Re: Climaveneta Chiller problem
does it have phase protection??- swap phases over in case compressors running backwards
-
21-11-2013, 07:24 PM #4
Re: Climaveneta Chiller problem
check the presence of three phases before\after on compressors contactor.
-
22-11-2013, 01:55 AM #5
Re: Climaveneta Chiller problem
ok frens..
today i will check and revert back to you....and any body have service manual of this model number..it will be highly appreciated..
-
23-11-2013, 01:15 PM #6
Re: Climaveneta Chiller problem
Dear frens..still the chiller had same problem
Chiller No. 1
Compressor of circuit no 4 trips with in a minute and shows Compressor fault error.
We are running this chiller by isolating the fault circuit.
CHILLER NO- 2
Compressor of circuit no 3 and 4 trips with in a minute and shows Compressor fault error.
We are running this chiller by isolating the fault circuit.
only 8 compressor were working now..if some body have service manual of this chiller then i will be
highly obliged.
-
23-11-2013, 04:46 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Climaveneta Chiller problem
Power source quality could be a issue!
Check voltages, voltage drop and balance of phases!
-
24-11-2013, 01:07 PM #8
Re: Climaveneta Chiller problem
new units. first start. compressor blocked. it is very strange! do you check power supply?
-
08-12-2013, 02:07 PM #9
Re: Climaveneta Chiller problem
What about the refrigeration charge? Is it charged by factory with HFC or nitrogen?
-
09-12-2013, 02:15 PM #10
Re: Climaveneta Chiller problem
@Murre: It was charged by Factory HFC...i found expansion valve is not working..