    Climaveneta Chiller problem



    Hi frens...
    we had installed two Climaveneta chillers on the Hospital, Model number: NECS-N/D/B 2818 and the S/NO:32023515

    the problems found on the chillers are as follows:-


    Chiller No. 1
    Compressor of circuit trips with in a minute and shows Compressor fault error..



    CHILLER NO- 2
    Compressor of circuit trips with in a minute and shows Compressor fault error.

    what will be the main reason behind it and waiting for the prompt reply..!!
    Cheers...



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Climaveneta Chiller problem

    Quote Originally Posted by anil130 View Post
    Hi frens...
    we had installed two Climaveneta chillers on the Hospital, Model number: NECS-N/D/B 2818 and the S/NO:32023515

    the problems found on the chillers are as follows:-


    Chiller No. 1
    Compressor of circuit trips with in a minute and shows Compressor fault error..



    CHILLER NO- 2
    Compressor of circuit trips with in a minute and shows Compressor fault error.

    what will be the main reason behind it and waiting for the prompt reply..!!
    Cheers...

    Hi, it could well be the compressor has overheated or the motor protector module is faulty (if that model has one)
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Climaveneta Chiller problem

    does it have phase protection??- swap phases over in case compressors running backwards

  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Climaveneta Chiller problem

    check the presence of three phases before\after on compressors contactor.

  5. #5
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Climaveneta Chiller problem

    ok frens..
    today i will check and revert back to you....and any body have service manual of this model number..it will be highly appreciated..

  6. #6
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Climaveneta Chiller problem

    Dear frens..still the chiller had same problem

    Chiller No. 1


    Compressor of circuit no 4 trips with in a minute and shows Compressor fault error.
    We are running this chiller by isolating the fault circuit.




    CHILLER NO- 2
    Compressor of circuit no 3 and 4 trips with in a minute and shows Compressor fault error.
    We are running this chiller by isolating the fault circuit.

    only 8 compressor were working now..if some body have service manual of this chiller then i will be
    highly obliged
    .

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Climaveneta Chiller problem

    Power source quality could be a issue!
    Check voltages, voltage drop and balance of phases!

  8. #8
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Climaveneta Chiller problem

    new units. first start. compressor blocked. it is very strange! do you check power supply?

  9. #9
    Join Date
    May 2010
    Location
    Finland
    Age
    44
    Posts
    9
    Rep Power
    0

    Re: Climaveneta Chiller problem

    What about the refrigeration charge? Is it charged by factory with HFC or nitrogen?

  10. #10
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Climaveneta Chiller problem

    @Murre: It was charged by Factory HFC...i found expansion valve is not working..