    I'm planning on expanding a phase change system to have a second and eventually third evap. I need a way to direct refrigerant (r404) to the various thermal heads on a duty cycle depending on each head's heat load and set temp. I'm thinking that the best way to do this is with solenoids and a cap tube manifold. A three-way solenoid would work for a dual head system. I'd like to keep it quiet if possible as the solenoids would be on a 10 second or less duty cycle. Would a servo be better? Can anyone recommend a solenoid, i've seen that LEDEX has some that are supposed to be quiet but I don't know if they would work with 404.
    Any help is appreciated.
    Oct 2001
    Nottingham UK
    5,127
    42
    Re: Multiple evap cap tube system
    Assuming that you have a fixed speed compressor?
    If you split your 'Evaporator' load into 3 and then control the amount of flow into each circuit by solenoid valves, how are you going to control the compressor and condenser duty when, say, 2 of your evaporators are not requiring any cooling (sol valves closed) ?
    I'm back on the Pale
    Mar 2013
    14
    I should have mentioned that the the heads have heater cartridges in them controlled by a independent PID loops. I'm using the solenoids to minimize the work required by the heaters. When two heads are not needed all of the refrigerant will go to the one that is active. The compressor is a fixed speed 1/4 hp.
    Oct 2001
    Nottingham UK
    5,127
    42
    Any chance of a sketch or drawing?
    Oct 2007
    manchester
    44
    5,707
    if your reducing the capacity of the evaps the you need to derate the outdoor unit- by means of an inverter drive or unloaders on the heads on bigger stuff
    Mar 2013
    14
    high side = 1/4" pipe
    suction line (purple) is 3/8"
    accumulator to compressor (blue) is 5/16"
    Using r404a we need to get down to -55C and would like to go as high as 200C being able to handle at least 300W at 0C. We've gotten down to -57C, i haven't run it up past 150C yet as our prototype evap was soldered not brazed.
    High side pressure is roughly 150psi and suction is around 15" Hg Vac.
    Oct 2007
    manchester
    44
    5,707
    I recommend a solonoid on the liq line before the evap to pump it down if your goin to 200 deg
    Mar 2013
    14
    You don't think leaving the hot gas valve wide open will be enough?
    Oct 2007
    manchester
    44
    5,707
    not if your taking your coil upto 200deg
    in low load conditions youll be operating on 1 coil and your compressor is suddenly well oversized- your tev will be sized to 33% of the outdoor capacity
    also you dont want any refrigerant in the evap if your heating your evap/conditioned space to +200deg
    check your pressures
    Sep 2009
    Iran
    483
    12
    solenoid valve on the liquid line before the evaporator to pump down it and also you can use (CPR) crankcase pressure control in suction line near compressor to protect you compressor from over load in starting time.
    I am sure you can use in 15 Hg vac. might you have to change spring inside CPR.