    Lightbulb Walkin Chiller pipe line Connection



    Hello,

    I am working as a resident Engineer in one of the main Hotel in Dubai
    Our cold room in main kitchen have 32 walk-in chiller,freezer and cooler
    These chillers are frequently tripped due to the high pressure alarm in compressor
    Building chilled water circuit line is using for the heat transfer in condenser section
    We found that building chilled water supply line is connected to ten chiller circuit suction line and all these chiller's discharge line is also connected to the building chilled water supply line.

    It means all chillers suction and discharge of condenser line is connected to the building chilled water supply line, there is an inline pump is also connected between the chiller discharge line and building chilled water line.

    Discharge line of the the chiller condenser is not connected to the building chilled water return lin

    could anyone please clarify that the pipe line connection is correct or wrong?

    Please check the attachment for better understanding....

    Thanks
    Attached Images Attached Images



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Walkin Chiller pipe line Connection

    Hi, ratheep

    welcome to RE forums ....

    you must be patient ... it is not necessary to post the same article in multiple threads ... it is very inconvenient to follow the same discussions over few threads ...

    each double posts we delete to keep forums tidy ....

    Furthermore we are volunteers here (making our daily bread at some other place/s) and for that reason each poster must be patient to get answer/s to his question ...

    I do believe you'll get some answer soon.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Walkin Chiller pipe line Connection

    Hi, ratheep

    How old is this plant .... do you have those problems since start?

    do you have the same problem during winter time?


    ... according to your sketch something is wrong with layout of inlet/outlet water pipes for condensers ....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Walkin Chiller pipe line Connection

    The chilled water flow to the condensers is wrong. The first condenser is OK but the return from this condenser then becomes the flow to the second condenser and so on. The heat picked up from the first condenser is added to the second condenser so by the time you get to condenser 10, you have very very little cooling effect.

    The pump is then dumping the return water back into the flow circuit instead of the chiller. This will add the heat rejected by the 10 walk-in chill rooms back into the chilled flow, raising it's temperature and reducing the cooling effect.
    A better system layout is attached
    Attached Files Attached Files

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Walkin Chiller pipe line Connection

    Franks drawing is the best option, also check if there are flow regulators fitted to the condensers, otherwise the first condenser might starve the others of flow

    al
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Nov 2013
    Location
    dubai
    Posts
    2
    Rep Power
    0

    Re: Walkin Chiller pipe line Connection

    untitled.JPG

    Sorry for the wrong layout...please check the updated layout..

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Walkin Chiller pipe line Connection

    Hi, ratheep


    Quote Originally Posted by ratheep View Post
    sorry for the wrong layout ..please check the updated layout...Attachment 10942


    even like this on updated drawing .... water piping is still wrong .... circulation pump outlet pipe should be connected to chilled water return line ....


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.