    condenser sizing



    Hi,
    can somebody give me some solutions on the given problems.
    1. original condenser has failed beyond repairs (running for 134a system). so an available condenser almost same capacity designed for R22 was used in its place but on running the sub cooling is found very high. Its hp is not coming down and the unit is tripping on hp. also there is no proper ventilation inside the room.
    readings-
    High pr- 225psi (and max250+)
    condenser incoming line- 185*F
    condensing line temp -80*F
    Amb - 77*F
    how to reduce the pressure, removed some gas but its a temporary again building up almost the same. purchasing a new condenser is costly affair, how to manage with the same.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: condenser sizing

    Go to luve.it and download their calculating program. its a good one.

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: condenser sizing

    Quote Originally Posted by tvrao View Post
    Hi,
    can somebody give me some solutions on the given problems.
    1. original condenser has failed beyond repairs (running for 134a system). so an available condenser almost same capacity designed for R22 was used in its place but on running the sub cooling is found very high. Its hp is not coming down and the unit is tripping on hp. also there is no proper ventilation inside the room.
    readings-
    High pr- 225psi (and max250+)
    condenser incoming line- 185*F
    condensing line temp -80*F
    Amb - 77*F
    how to reduce the pressure, removed some gas but its a temporary again building up almost the same. purchasing a new condenser is costly affair, how to manage with the same.
    what is the entering and leaving the air temperature of your condenser?