    McQuay Chiller PEH 126: Tripping



    Dear Fellow RE members,

    My name is Anggoro from Central Java, Indonesia.

    We operate several McQuay Chiller (PEH 126). I have to admit that they are not new chillers, these chillers has started their operation in 1995 - 1997. In general, they are still running properly.

    However, several time we experience tripping of chiller. The message in the display is: "LOW MOTOR CURRENT". Usually, we will reset the alarm and restart the chiller without any difficulty.

    I try to talk with local McQuay tech and they suspect that it is caused by power disturbances, CPU/controller failure or cable connection problem. In many occasions, I check our power monitoring system and there is no power disturbances (sag/swell etc) when it happen. Cable connection seems okey as well. So we suspect that the cause is CPU/controller.

    Does anyone in this community have any similar experiences? How do you solve the problem? Will replacing the CPU solve the problem?

    I will be very grateful to have any feedback and advice from any of you.

    Thank you very much.


    Your sincerely,

    Anggoro Yudho N



  2. #2
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: McQuay Chiller PEH 126: Tripping

    Is there a pcb with a row of black plug in relays on it, if so check the relay that enables the compressor

  3. #3
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: McQuay Chiller PEH 126: Tripping

    I recently had this problem on a different system and it turned out that the current transformers were weak and needed replacing.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: McQuay Chiller PEH 126: Tripping

    Quote Originally Posted by passandscore View Post
    I recently had this problem on a different system and it turned out that the current transformers were weak and needed replacing.
    Hi
    this would seem the right course of action
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: McQuay Chiller PEH 126: Tripping

    Quote Originally Posted by anggoro View Post
    Dear Fellow RE members,

    My name is Anggoro from Central Java, Indonesia.

    We operate several McQuay Chiller (PEH 126). I have to admit that they are not new chillers, these chillers has started their operation in 1995 - 1997. In general, they are still running properly.

    However, several time we experience tripping of chiller.
    Is this happening on several chillers or only one?