    Mitsubishi r2 test procedures ? And test results ?



    Hiya all

    I have installed 4 Mitsubishi r2 systems pury p350 ... I've had all units running in both modes with decent temps in both modes = 10*c in cooling 40*c in heating .
    I've since added all units to g50 central controller and all units are visible and working .without any error codes anywhere .

    However now 2 months later we are getting various call back issues regarding temps on the local controllers never getting near the 26*c that they ask for , people saying it says HEAT STANBY a lot , also that one unit blows cold when local controller says heat & heats when local controller says cool ( I doubt this is even possible I think it's more likely operator error ??)

    I have noticed that the temp drop in the building is very high at night .. The average temp in some of the areas first thing in the morning is as low as 10*c despite these areas getting up to 24*c-26*c during the day .

    We are due back to site Saturday to test all units in heat modes and provide our test results ... PLEASE could someone advise me best procedure to test systems ? and also what should be my air off -air on difference be ? etc and any other factors I could run checks and tests on . Will it be best to TEST MODE the systems ??

    I have to prove that what's installed is running right and doing the job it's being asked to do !!

    Thanks for any replies



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Mitsubishi r2 test procedures ? And test results ?

    And what makes you think that you will be getting more answers with spamming all forums with your same question? It is not polite to do that. Makes you to look like very selfish person, and who likes to help selfish persons.

    And how you think that all answers will be on same place? Not very productive approach! Dont you think?
    Last edited by nike123; 14-11-2013 at 05:20 PM.

  3. #3
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    As I state on my profile line .. I'm new to this forum !!
    I thought that would be the correct way to get my question read by someone who may be able to help . If there is an code of conduct to stick to accept my apologise .

    As for selfish ?? Not really !!!! ..... But thank you for your swift reply to let me know your thoughts .

    Good luck in your quest to get a decent job !!!

    Feel free to contact my company I will look at your cv

  4. #4
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi r2 test procedures ? And test results ?

    Take M-net checker and look at all system. Or you need ****ing lot of experience to find whats happend by hands.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi r2 test procedures ? And test results ?

    http://www.mediafire.com/download/91...(HWE10050).pdf
    click on link above for service manual

    is there any lossnay units- is there fresh air onto the indoors?- fit duct heater or slow fan down and programme time schedule for when staff in- programme ac to start earlier to reach setpoint

    are the filters clean- are the controllers set correct, ie not cool 26??

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi r2 test procedures ? And test results ?

    It sounds like you have port numbers crossed. When you commissioned the system did you collectively put all indoor units on cool mode and then all indoor units on heat mode?
    If you commissioned them this way rather than testing them individually on both modes then there's a chance the port numbers have become mixed up, this is a very common problem on systems after they have been commissioned.

    Do you have a M-net checker, to look at the system? If you do then this can be rectified within 1 hour.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Mitsubishi r2 test procedures ? And test results ?

    Hi, Cmsaircon

    Welcome to RE forums ....


    here you can find little more about RE rules ... http://www.refrigeration-engineer.com/rule


    Quote Originally Posted by Cmsaircon View Post
    As I state on my profile line .. I'm new to this forum !!
    I thought that would be the correct way to get my question read by someone who may be able to help . If there is an code of conduct to stick to accept my apologise .

    As for selfish ?? Not really !!!! ..... But thank you for your swift reply to let me know your thoughts .

    Good luck in your quest to get a decent job !!!

    Feel free to contact my company I will look at your cv
    it is not necessary to post the same question at multiple forums ...

    that confuse you and other people replaying to you ... it is hard to follow conversation ...

    then, sometimes you need to be patient ... we all are working people (making our daily bread at some other places like you) thus we are volunteers here and sometimes have no time to visit forums regularly ... also we are trying to give a good and accurate advice - we all know what is dead end ....

    generally here are very good girls&guys like humans or like professionals, believe me

    As per nike123 ... if you really need a good service man, he is your man - I guarantee for him - sometimes he is too fast and to furious, but never evil just contrary ... unfortunately, recently here jobs are very slow ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    Thanks guys for the replies ... Yes there are lossnays fitted to supply fresh air .
    YES I did test all units in same mode at same time :0( ... I will check ports and test units 1 at a time first job !! M-net checker ?? I've never come across this ? Is it a specialised tool ?

    We will be doing a full filter clean too on Saturday so won't know filter condition til then .

    I've been advised to put some of the units on night set back because of the dramatic temp drop between close / open times of the office .. Have you heard of this ??

  9. #9
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    Thanks Josip

    I'm just getting hang of this forum and finding it brilliant so far .. Really good to be able to ask questions to really experienced guys from the industry .

    Look forward to continuing on here

  10. #10
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi r2 test procedures ? And test results ?

    The M-net monitoring tool is a tool that plugs into the 30vdc m-net line and enables you to see all of the operating parameters, including sensors, lev positions, connection info etc etc.

    Best thing to do would be to put all indoor units on test cooling, after 15 mins put 1 indoor on test heating and wait to see if this starts heating. If it does put it back to cooling mode and then move to the next indoor unit and put this on heat mode and keep repeating the procedure until all indoors have been tested.
    It may take a while to complete but I'm sure you will find this to be your problem.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  11. #11
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    Brilliant ... Thanks very much .

    Saturday I will no where to start looking and things to check .

    Mnet monitoring tool sounds like a piece of kit I would be interesting in using . Do you know best place to get this ?
    Cheers

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi r2 test procedures ? And test results ?

    Your welcome.

    If you have any other problems with the system, post back and we will try and help you.

    The monitoring tool is very difficult to get hold of, unless of course you are a partner of Mitsubishi and spend around 250K a year on their products.
    Then you have to go on the training course and then you get it.... But you can get all of the data from the SW1 dip switches on the outdoor board.
    Get your self a city multi service manual and the dip switch settings are in the back of the book.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  13. #13
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    I work as a sub contractor for someone that is a partner , I'm going get on them to get me on a courses ..

    Cheers

    Will let you know how it goes saturday

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi r2 test procedures ? And test results ?

    setback temperature is programmed on the g50 so when the kit is off- you set the setback to say 16deg to prevent the room temp from dropping below this- vams should have a inline duct heater downstream of the duct- ideally thyristor controlled to maintain a minimum supply air of 16deg- set the vams to come on later than the rest of the kit, maybe switch the vams off for an hour- check your not gettin too much fresh air onto the unit, ensure sw1 ,1 is on on each indoor -if they have a local remote- otherwise a room sensor can be bought and plug it into where the return air sensor is plugged in, also a high ceiling void with uninsulated ceiling tiles,gaps in the cladding of the roof is a good cause of performance issues

  15. #15
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    Thanks again

  16. #16
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    Quote Originally Posted by Cmsaircon View Post
    Hiya all

    I have installed 4 Mitsubishi r2 systems pury p350 ... I've had all units running in both modes with decent temps in both modes = 10*c in cooling 40*c in heating .
    I've since added all units to g50 central controller and all units are visible and working .without any error codes anywhere .

    However now 2 months later we are getting various call back issues regarding temps on the local controllers never getting near the 26*c that they ask for , people saying it says HEAT STANBY a lot , also that one unit blows cold when local controller says heat & heats when local controller says cool ( I doubt this is even possible I think it's more likely operator error ??)

    I have noticed that the temp drop in the building is very high at night .. The average temp in some of the areas first thing in the morning is as low as 10*c despite these areas getting up to 24*c-26*c during the day .

    We are due back to site Saturday to test all units in heat modes and provide our test results ... PLEASE could someone advise me best procedure to test systems ? and also what should be my air off -air on difference be ? etc and any other factors I could run checks and tests on . Will it be best to TEST MODE the systems ??

    I have to prove that what's installed is running right and doing the job it's being asked to do !!

    Thanks for any replies
    Are your additional refrigerant calculations correct, double check these. Check your BC ports as stated by others, also try and prevent the room temperature dropping to 10c, must be badly insulated building. If the system has to start with 0c ambient and 10c indoor ambient, it'll probably take most of the day to bring the temperature up, so if you think you got problems now, wait till the winter kicks in! What about the diversity? I've found some systems at 150% struggle in winter time, constantly defrosting. I think as an installer all you can really do is check the refrigerant calculation and have them verified by Mitsubishi Electric and check the BC ports are correctly addressed. If you've operational issues after that then I'd call in Mitsubishi but i'd be a bit concerned that the building is 10c in the morning!

  17. #17
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Mitsubishi r2 test procedures ? And test results ?

    Thanks to all your replies, I did find that 2 units were set incorrect ports hence the the strange temps ,
    I ran all units in heat mode and all managed to get to there target set points eventually some longer than others ... I've raised the concern to the client as 4 rooms had a start temp point of 12*c on sat morning and its not even hit winter yet !! I've set these rooms to a 16*c night set back for now

    But all in all everything is working and have fine and good test results to show this now .

    Thanks again to all your comments

  18. #18
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi r2 test procedures ? And test results ?

    Thanks for updating us, glad you got it sorted.
    The difference between genius and stupidity is that genius has its limits.

    Marc