Mitsubishi heavy industries 407 VRF compressor fails
Hi all,
From last year........
We have recently taken looking after a company with lots of Heavy industries VRF on
407, the few 3pipe systems have been destroying compressors within 12 months one recently in 5 months ! It's only the 3 pipe systems that have the problem and I have been told other sites have had the same issue with these systems -FDCP280HKXRE2A !
From today....... One system fractured a pipe in the condenser so we repaired and replaced with fresh gas. The system ran for a few hours then the compressor failed. Replaced compressor the new one lasted 3 days argh !!!
Any ideas pleeeease ?????
Matt
-
12-11-2013, 05:47 PM #2
Re: Mitsubishi heavy industries 407 VRF compressor fails
mitsi heavy warranty states about cutting out a section of a brazed joint,and use of burnout driers- and removing them after approx 1 week of running
http://www.mediafire.com/download/s8...compressor.pdf
click on the link for more info
-
12-11-2013, 06:28 PM #3
Re: Mitsubishi heavy industries 407 VRF compressor fails
Lol...our command wash out bad oil one week in time without unpipe 1360 KX6.
http://www.youtube.com/watch?v=jwX6T5EegOA
Idea is call smbd with "know how" MentePC, SuperLinkCheker, and give them money camping beer whores whatever)))
-
12-11-2013, 06:35 PM #4
Re: Mitsubishi heavy industries 407 VRF compressor fails
http://www.3dair.co.uk/DOWNLOADS_may...20&%20KXR4.pdf
http://www.ampair.co.uk/files/FDCP22...e%20Manual.pdf
service manuals
if a compressor fails u need to do an acid test, crankcase heaters energised for 24 hrs and inverter circuit replaced with new compressorLast edited by install monkey; 12-11-2013 at 06:37 PM. Reason: sorry RusBuka cant give rep points for that excellent answer!
-
12-11-2013, 09:56 PM #5
Re: Mitsubishi heavy industries 407 VRF compressor fails
in MHI KX i never see problems in IGBT or IPM. With burned, over current or locked compressors every time electric parts was fine. Its not daikin vrv2-3, if you have burned comp. you always have PCB what you can throw away.
p.s. install monkey you can see what happens with 3D compressors in KХ6 systems. All bearings was locked.
-
13-11-2013, 11:31 AM #6
Re: Mitsubishi heavy industries 407 VRF compressor fails
My little fault. KX2 is without Menta. Only SLCheker and hands. In 3 pipe KX2 was trouble with oil return from PFD blocks. In KX4 this trouble was fixed.
sow, run forest, run )
-
14-11-2013, 09:48 PM #7
Re: Mitsubishi heavy industries 407 VRF compressor fails
One more try then I'm running like the wind !
Funny how MHI can make such a massive heap of **** and just shrug their shoulders in a tough luck manner !
Reports from a local university that had stacks of these installed that they had all the same issues due to oil return, problem there on is it only gets worse as each burnt out compressor just adds that little bit more contamination.
Also the indoor pipework temps vary so much as you go through it all, the oil must be clogged up acid to the eyeballs !
-
15-11-2013, 07:40 AM #8
Re: Mitsubishi heavy industries 407 VRF compressor fails
You know how many Daikin VRV2 and VRV3 3 pipe was dead by arrive? Or how often inverter in FGL V series dead by month.
All manufacturers were problems in the beginning of the thorny path. Someone makes conclusions and improves, someone never changes)