    Split system no sirculation ?



    Hi all,
    New here so please bear with me.
    I have a Ecoair split system about 15month old, model ECO1211S
    It seems to work ok in cooling mode but in heat mode after 30min running the gas line from condenser is too hot to touch but no heat from indoor unit. Gas line at indoor unit is only luke warm. If left running outside unit starts to squeal so I have to shut it down. Was told it’s likely to be refrigerant loss but when a retired engineer checked he said the pressures seem normal.
    No damage anywhere to lines so what would stop the circulation ?
    Someone else said its rubbish so scrap it, just naffed that it is out of guarantee.
    One or two pointers as to what to look for would be much appreciated.
    Thanks in anticipation.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Split system no sirculation ?

    Dirty filters, not so likely if pipes got cool by indoor unit.
    Short of refrigerant. Only way to be sure is to remove it with a special machine and weigh it to see if it has the manufacturers charge in plus and additions due to pipe length.
    Compressor worn.
    Reversing valve not making full travel in heating mode.

    Favourite would be refrigerant shortage, especially if it was a diy install.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Split system no sirculation ?

    indoor coil sensor- in heating mode it should speed up the indoor fan
    normal operation in heating mode would be indoor fan runs at a low speed- compressor starts after a 3 min delay- after about 2 mins the indoor coil will be at 30degrees, then the indoor fan will speed up, typical for coil sensor to cook itself

  4. #4
    Join Date
    Nov 2013
    Location
    united kingdom
    Posts
    2
    Rep Power
    0

    Re: Split system no sirculation ?

    Thanks for the responses guys.
    Checked filters all ok, not sure if it's possible to check valve travel without removal.
    Fan does run at low speed initially but pipes at evaporator never reach 30 degrees. putting fan on higher speed manually has no effect. The gas line from the condenser is very hot for about 6 to 10 feet then cools off to nothing as if it's a circulation problem, if a low charge would cause this it's looking likely monkey spanners is right. I do remember that the initial installation used a 10mtr pipe set and it said that this was the max without additional charge so assume only a small drop would cause problems ? does this seem logical?
    Thanks again.