11-11-2013, 09:12 AM #1
fridge freezers not cycling on and off - please help!!
I have recently been experiencing fridge freezers with mechanical vt9 thermostats not ever cycling on and off, I have tried changing the thermostats on them but it doesn't make any difference at all, they just stay on all the time! Also I have changed the compressor thinking that was the problem but it just never works! Any help with this would be appreciated as its becoming a common fault for me
12-11-2013, 12:27 PM #2
Re: fridge freezers not cycling on and off - please help!!
anyone??? Im really stuck here!
12-11-2013, 01:50 PM #3
Dont usually work on domestics but it could be possible that the tstat is controlling a relay that is stuck closed,also if from what i understand it they are frost free fridges i dont think a vt9 is suitable as the cutout is too low ,need a vxo on these -15 as opposed to -26 cutout.Dont think the feeler is in direct contact with the coil on the frost free cases
12-11-2013, 10:59 PM #4
Some times what causes that, is a gas leak (undercharge), the probe of thermostat never reaches the cutout temp because saturated liquid never reaches on to it.
13-11-2013, 10:11 AM #5
It's def reaching the cut-out point, the fridge is at -10 and freezer is at -40, also its not a frost free system they are both just regular fridge freezers, basically a thermostat and a compressor, ill try the relay on the compressor and get back to you. thanks for the help
13-11-2013, 11:47 AM #6
think they were low on gas, put a charge in each and they cut out, just waiting on them coming back on now