Results 1 to 5 of 5
  1. #1
    fatboysims's Avatar
    fatboysims Guest

    Oil traps for r407c



    Hi there,
    question do you needs oil traps on r407c air conditioning systems, I now on most systems they should be every 10m's or so, I was told that oil traps not needed on r407c is this correct!!!

    many thanks.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Oil traps for r407c

    highcool splits, airedale units do, most brandsof splits dont, ie daikn,fujitsu,mitsi,tosh
    check the installation manual

  3. #3
    fatboysims's Avatar
    fatboysims Guest

    Re: Oil traps for r407c

    It's not for an install just a general question, because I think 410 is different again! Cheers for your reply.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Oil traps for r407c

    Oil traps are used to ensure that the oil returns to the compressor where lengthy vertical suction lines are installed and the evaporator is installed below the condenser/compressor. They are generally used on refrigeration, but not so much on air conditioning systems.

    The type of refrigerant is not usually the deciding factor.

  5. #5
    Join Date
    May 2010
    Location
    Finland
    Age
    44
    Posts
    9
    Rep Power
    0

    Re: Oil traps for r407c

    No matter if it is refrigeration or air condition system. Allways use oil trap's to secure that the oil is returning to the compressor.