Oil traps for r407c
Hi there,
question do you needs oil traps on r407c air conditioning systems, I now on most systems they should be every 10m's or so, I was told that oil traps not needed on r407c is this correct!!!
many thanks.
-
10-11-2013, 10:09 AM #2
Re: Oil traps for r407c
highcool splits, airedale units do, most brandsof splits dont, ie daikn,fujitsu,mitsi,tosh
check the installation manual
-
10-11-2013, 10:22 AM #3
Re: Oil traps for r407c
It's not for an install just a general question, because I think 410 is different again! Cheers for your reply.
-
11-11-2013, 01:28 PM #4
Re: Oil traps for r407c
Oil traps are used to ensure that the oil returns to the compressor where lengthy vertical suction lines are installed and the evaporator is installed below the condenser/compressor. They are generally used on refrigeration, but not so much on air conditioning systems.
The type of refrigerant is not usually the deciding factor.
-
08-12-2013, 01:57 PM #5
Re: Oil traps for r407c
No matter if it is refrigeration or air condition system. Allways use oil trap's to secure that the oil is returning to the compressor.