    Mitsubishi Inverter 12k shuts down after a few minutes in heating mode



    Hi again,
    So I have a case of a mitsubishi inverter mini-split that stops working after a whyle (not even the fans rotate, although it stays ON) in heating mode (in automatic it doesn't heat at all), in heat mode it works fine for a few minutes than it stops and never restarts, unless you turn it off and on again (and it works for some more minutes and stops).

    I suspect a thermostat problem but since it does cool normally (althought the client said that he feels that it's not as cool as it was before) I don't know.

    This unit had a gass leak some time ago that was corrected and we applied a new full charge to it, i don't think it's related but then again, I don't know.

    Any help is appreciated, thanks in advance.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    doyou have model number??

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    in heating mode the fan runs in low low speed until the indoor coil sensor reaches 33 deg then it speeds up, cooling mode the fan runs in hi or low

  4. #4
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Thanks for the replys, sorry i don't know the reference, i think it's n MXZ but I could be wrong, about the slow rotation of the fans, they stop afeter a whyle, stop as in full stop, and you can't sense anymore the warm air, it just stops functioning.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    http://www.mediafire.com/download/cp...OC316revE).pdf
    click on the link above for mxz service manual

  6. #6
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Quote Originally Posted by install monkey View Post
    http://www.mediafire.com/download/cp...OC316revE).pdf
    click on the link above for mxz service manual
    Thanks for the link but i got the reference mixed, it's nopt a multi-spli just a normal mini-spli I think it's the MSZ-HJ35VA but i could be wrong but this time i think i got it right, sorry for the mess up..

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode


  8. #8
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Thanks, going to read a bit..

  9. #9
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Hi again, and thanks for the replies, so I went to see the mini-split yesterday (it actually was a Mitsubishi Heavy Industries DXK12Z3-S, my bad).

    Many strange things, first there appeared to be no r410a leaks, but the pressure OFF/Cooling/heating was always the same (around 14.5 Bar),compressor not pumping? clogged? thermostate not giving the right order?
    Also, it didn't cool anymore , wich was hard to see since it was a cold day anyways but I didn't feel any "cold" air being blown out (forgot the thermometer, sad, so sad..).
    In heating mode it did heat but aftera whyle (let's say 8 minutes) it slowly stopped the fans and started blowing almost "cold" air, not warm at all and the room was far from being warm (I set the temp to 30şC and there was not even 20şC in the room).
    Since it did work well before, I assumed all connections were OK, I did check them there seems to be no problem with that.
    So we called the Mitsubishi assistance and are waiting to see, I'll comment when I know but my money is either on a broken compressor or a clogged one (since it was a pre-instalation there might have been dust in the cooper pipes, we did blow it with N but that might not have "cleaned" them interely.

  10. #10
    Join Date
    Feb 2005
    Location
    Australia
    Posts
    123
    Rep Power
    21

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Quote Originally Posted by LChaminés View Post
    Hi again, and thanks for the replies, so I went to see the mini-split yesterday (it actually was a Mitsubishi Heavy Industries DXK12Z3-S, my bad).

    So we called the Mitsubishi assistance and are waiting to see, I'll comment when I know but my money is either on a broken compressor or a clogged one (since it was a pre-instalation there might have been dust in the cooper pipes, we did blow it with N but that might not have "cleaned" them interely.
    If it's a MHI unit put it into Service mode and check the stop code history, that will give you a better idea of what has been happening.
    To access service mode turn off the AC power to the unit and wait 2-3 minutes. Then press and hold in the on/off button on the Indoor unit and at the same time get someone to turn the power back on to the indoor unit. It helps if you have 2 people to do this, otherwise find a way to jam the button in whilst you go and turn the power back on (The On/Off button is part of remote control receiver window). If you have done this correctly the Indoor unit should beep and the Run & Timer light will flash together for 1.5 seconds. Then set the remote control to Cooling mode, Lo fan setting and 21°C setpoint. Count how many times the Run light flashes after the long flash and how many times the Timer light flashes, this gives you a 2 digit code to look up later. You can keep changing the remote setting from Cooling Lo fan 21 all the way up to 30° settings for the last 10 protective stop codes. Let us know what they are and we can help you.
    Note Do not count the long flash, this is just the indicator that it is in service mode and that it is the start of the sequence.

  11. #11
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Quote Originally Posted by ozairman View Post
    If it's a MHI unit put it into Service mode and check the stop code history, that will give you a better idea of what has been happening.
    To access service mode turn off the AC power to the unit and wait 2-3 minutes. Then press and hold in the on/off button on the Indoor unit and at the same time get someone to turn the power back on to the indoor unit. It helps if you have 2 people to do this, otherwise find a way to jam the button in whilst you go and turn the power back on (The On/Off button is part of remote control receiver window). If you have done this correctly the Indoor unit should beep and the Run & Timer light will flash together for 1.5 seconds. Then set the remote control to Cooling mode, Lo fan setting and 21°C setpoint. Count how many times the Run light flashes after the long flash and how many times the Timer light flashes, this gives you a 2 digit code to look up later. You can keep changing the remote setting from Cooling Lo fan 21 all the way up to 30° settings for the last 10 protective stop codes. Let us know what they are and we can help you.
    Note Do not count the long flash, this is just the indicator that it is in service mode and that it is the start of the sequence.
    Oh, too bad I didn't knew that 2 days ago but thanks, I'll keep that in mind, I'm probably
    returning there in a week or two and I'll do that so I can post here, once again thanks for all the replies, I'll report in a week or so.

  12. #12
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Just an update on this, the mitsubishi technician went to check the machine and said it was either dust or water/humidity, so we did a 24 hour vacuum and fresh charge, and it's been working well, althought we still have to wait to see if there's no permanant damage to the AC

  13. #13
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    24 hour vacoum?

  14. #14
    Join Date
    Sep 2013
    Location
    Portugal
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Inverter 12k shuts down after a few minutes in heating mode

    Quote Originally Posted by Greek_engineer View Post
    24 hour vacoum?
    Recomended by mitsubishi technician, although if there's "garbage" in a capilar (maybe this is not the right word) the all machine may not work