    ReciprocatingChiller question
    photo2.jpgBeen racking my brain on these questions
    1. Approach temp=
    2.cooler flow rate=gpm
    3 RISE
    4. COOLER PRESSURE DROP = PSI
    Also what will the net refrigeration effect be if there is a fouling factor of 0.0025
    Apr 2008
    Canada
    253
    4
    Re: ReciprocatingChiller question
    Recommend re-phrasing the question!
    Aug 2009
    utah
    83
    15
    How would I re-phrase question
    Aug 2009
    utah
    83
    15
    Quote Originally Posted by passandscore View Post
    I forgot to add diagram. Sorry for ther confusion! My mistake
    Auckland
    74
    3,357
    37
    approach refers to SST versus water entering chiller.
    Cooler flow rate in US gallons per minute, governs the total performance on system.
    Rise refers in general to the temp change in water flowing through chiller.
    Cooler pressure drop or delta P, is a double check on water flow rate, as chiller manufacture would has publish data on flow rates at given pressure drops.
    Fouling factor is the maximum allowable fouling effect on chiller tubes, even closed circuit chilled water systems gunge up, this effects the heat transfer and reduces chiller capacity.
    magoo
    Aug 2009
    utah
    83
    15
    For rise I came up with 11 degrees
    for app0roach i came up with 15 degrees
    cooler flow rate came up with 110.7 gpm
    fouling factor came up with 48 tons
    Was anybody close to my answers
    Auckland
    74
    3,357
    37
    using figures off drawing and stated water flow rate at 110.7 USgpm, converted to SI, I get 178.62 Kw NRE ( net/ nominal refrigeration effect ) or 50.78 tons
    OK SI metric system,,, Q (water) = L/sec x Delta TK' x specific heat 4.192 kj/kg = Kw refrig
    Cannot remember specific heat value of water in imperial.
    Aug 2009
    utah
    83
    15
    how close were you to this answer I had cooler flow rate came up with 110.7 gpm