    Radford Scroll Pack - HP switch?



    Can't find a HP cut-off on a Radford HT scroll pack (R404a). Any ideas if it's placed somewhere unusual? Or is it possible they were installed without a mechanical HP switch? It was installed in '97.



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Radford Scroll Pack - HP switch?

    Check the electrical schematic. Perhaps you're correct! I assume you followed the highside piping and checked the control circuit?

  3. #3
    Join Date
    Mar 2009
    Location
    UK
    Posts
    29
    Rep Power
    0

    Re: Radford Scroll Pack - HP switch?

    Yes mate, checked everywhere around the pack. All the pressure switches on the high side just controlled the condenser backup.

    I thought, or perhaps assumed, it were a legal requirement to have a mechanical HP cut off on systems this size?

  4. #4
    Join Date
    Sep 2013
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Radford Scroll Pack - HP switch?

    hp setting sometimes controlled by elm/rdm controller via pressure transducer,forcing pack into standby mode.
    you will find compressors are fitted with fixed hp switches