    distributor frost



    Hi Sirs,
    I've just done a dehumidifier test. The frost is serious at the place of distributor outlet tubes of DX cooling coil. The pressure before distributor is 5 bar(R22) gauge pressure which should not cause frost. Suction temp is too high 20C,the dischange pressure is 14bar gauge.I think the distributor is with some problem. Blocked or large pressure loss. how do you think?

    rgds
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: distributor frost

    good day
    the dicharge pressur is normal . but tell me : is there frost after the tev? cause this means that you have partial blockage in tev
    other cause is : you missed the size of tev, or you must check the opening of the needle orifice ,slightly turn the screw clock wise to increase refrigerant flow, see if it become better
    , i think it starved refrigerant
    good luck