    so damaged burn out compressor



    HI
    i recieved a window type air cond
    2 ton
    cooling only
    i check ed the compressor so the reading wasnt correct
    also there were leaks with strange green material on the pipes of the condensor on the leak places
    i checked the resistance between compresoor lead
    R lead was not giving read
    so i removed the compressor
    then
    i cut the case of the compressor
    and i seriously surprised with how damage happened to it
























    over load !!!!!!!!!!!!!!!!!!!!!
    Last edited by kefah; 30-10-2013 at 08:34 PM.



  2. #2
    Join Date
    Apr 2008
    Location
    north west runcorn
    Age
    57
    Posts
    28
    Rep Power
    0

    Re: so damaged burn out compressor

    That is f__ked

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: so damaged burn out compressor

    see your hands better- wear doctors gloves or barrier cream- oil can be acidic
    Quote Originally Posted by kefah View Post
    HI
    i recieved a window type air cond
    2 ton
    cooling only
    i check ed the compressor so the reading wasnt correct
    also there were leaks with strange green material on the pipes of the condensor on the leak places
    i checked the resistance between compresoor lead
    R lead was not giving read
    so i removed the compressor
    then
    i cut the case of the compressor
    and i seriously surprised with how damage happened to it
























    over load !!!!!!!!!!!!!!!!!!!!!

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: so damaged burn out compressor

    Never seen one that bad!
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: so damaged burn out compressor

    Did that thing have an 10mm bolt as a fuse?? Was there any cable left supplying it?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: so damaged burn out compressor

    Electrical power installations in Iraq sometimes looked like this when i was there 1989:



    Possible now? You think this is fused properly?
    Last edited by nike123; 31-10-2013 at 08:51 AM.

  7. #7
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: so damaged burn out compressor

    Quote Originally Posted by NewmanRef View Post
    Did that thing have an 10mm bolt as a fuse?? Was there any cable left supplying it?
    it was the internal overload

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: so damaged burn out compressor

    I've seen that black stuff before when R407c ends up with moisture in it.

  9. #9
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: so damaged burn out compressor

    this unit had burnout compressor before
    so it been replaced before 3 years with the current burn out compressor

    i know the technesians who replaced it
    they replaced the first one
    with the current compressor without flushing the system
    and with in sufficient vacuum
    i wander where does the green stuff on the leaks place came from

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: so damaged burn out compressor

    Quote Originally Posted by kefah View Post
    i wander where does the green stuff on the leaks place came from
    I suspect it could be a UV dye http://www.spectroline.com/content/hvacr-products

  11. #11
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: so damaged burn out compressor

    Hi
    wow ......that is serious burning !
    this was either low voltage cooking,
    or repeated short circuit ruptures .
    acid and copper ,or copper oxidation , would all show up as green guk.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  12. #12
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: so damaged burn out compressor

    thank u all
    i hit the compressor winding with hammer
    the winding are from aluminuim not copper