Results 1 to 12 of 12
Thread: so damaged burn out compressor
-
30-10-2013, 06:43 PM #1
so damaged burn out compressor
HI
i recieved a window type air cond
2 ton
cooling only
i check ed the compressor so the reading wasnt correct
also there were leaks with strange green material on the pipes of the condensor on the leak places
i checked the resistance between compresoor lead
R lead was not giving read
so i removed the compressor
then
i cut the case of the compressor
and i seriously surprised with how damage happened to it
over load !!!!!!!!!!!!!!!!!!!!!Last edited by kefah; 30-10-2013 at 08:34 PM.
-
30-10-2013, 08:53 PM #2
Re: so damaged burn out compressor
That is f__ked
-
30-10-2013, 09:00 PM #3
-
30-10-2013, 10:52 PM #4
Re: so damaged burn out compressor
Never seen one that bad!
Mostly found in Oxfordshire, UK :)
-
31-10-2013, 06:53 AM #5
Re: so damaged burn out compressor
Did that thing have an 10mm bolt as a fuse?? Was there any cable left supplying it?
-
31-10-2013, 08:40 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: so damaged burn out compressor
Electrical power installations in Iraq sometimes looked like this when i was there 1989:
Possible now? You think this is fused properly?Last edited by nike123; 31-10-2013 at 08:51 AM.
-
31-10-2013, 11:32 AM #7
-
31-10-2013, 11:57 AM #8
Re: so damaged burn out compressor
I've seen that black stuff before when R407c ends up with moisture in it.
-
31-10-2013, 12:07 PM #9
Re: so damaged burn out compressor
this unit had burnout compressor before
so it been replaced before 3 years with the current burn out compressor
i know the technesians who replaced it
they replaced the first one
with the current compressor without flushing the system
and with in sufficient vacuum
i wander where does the green stuff on the leaks place came from
-
31-10-2013, 05:16 PM #10
Re: so damaged burn out compressor
I suspect it could be a UV dye http://www.spectroline.com/content/hvacr-products
-
01-11-2013, 11:34 AM #11
Re: so damaged burn out compressor
Hi
wow ......that is serious burning !
this was either low voltage cooking,
or repeated short circuit ruptures .
acid and copper ,or copper oxidation , would all show up as green guk.
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
03-11-2013, 03:30 PM #12
Re: so damaged burn out compressor
thank u all
i hit the compressor winding with hammer
the winding are from aluminuim not copper