    Post Mitsubishi VRF



    Hi I'm new so not sure if I'm posting this in right section.
    I have just turn't on a new system I installed on a 17 fan coil system and a the units keep displaying heat standby and then when they heat they throw out very little heat. It's a 300+400 condenser which has taken 48kg added R410a (calculated by Mitsubishi) + 20kg pre charge. Could it be short of gas still? I need to get this sorted asap as handover is tomorrow! If I run half I get some heat off but still not what it should be. Please help!!
    Ryan



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Mitsubishi VRF

    Have you had the crankcase heaters energised for the recommended length of time? If not, the system will run in protective limited output mode.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Oct 2013
    Location
    Uk
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi VRF

    We had the issue after turning on 2 hours after power was on and is doing it now even though has been power on since Friday.

  4. #4
    Join Date
    Oct 2013
    Location
    Uk
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi VRF

    Please someone help!

  5. #5
    Join Date
    Nov 2008
    Location
    birmingham
    Posts
    155
    Rep Power
    19

    Re: Mitsi heat standby problem

    Hi Ryan,

    Will the system run in test mode?

  6. #6
    Join Date
    Oct 2013
    Location
    Uk
    Posts
    4
    Rep Power
    0

    Re: Mitsi heat standby problem

    I put units on test through controller and they done the same thing so very little heat.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi VRF

    is the compressor ramping up, check on the outdoor pcb target freq,actual frequency - comfirm number of indoors connected- check all valves open- also pipe sensor values- all accessed via dipswitches

  8. #8
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Mitsubishi VRF

    Do you have any fresh air onto the indoor fan coils? If so is it pre-heated? Balanced? Are indoors in any kind of boxing? Check not recirculating in boxing. What sort of capacity is the system running at? What air on and off temps are you actually getting? Room temp?

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Mitsubishi VRF

    Did you followed start up procedure as it is written in installation manual? Adressing is OK?
    What is outdoor unit model No?

  10. #10
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi VRF

    Loooool))))
    1. What mitsubishi? MHI or ME
    2. Indoor and outdoor units names.
    3. Outdoor and indoor temperature.
    4. Equivalent length from OU to farthest IU (42 kg its a ****en lot)

    p.s. somebody in UK help him with M-net or Menta for money.