    Arneg Chiller cools after witched off overnight



    Hi

    I hope someone can shed some light on the issue I have.

    And also Thanks for the help in advance.



    I have a client who has an arneg display chiller with a remote condenser. systems been working fine for about 2 years and has had a clean and service etc (done every year by us) suddenly the system has generated an issue where it stops cooling.

    It stops cooling, and when switched off overnight, and switched on again in the morning, it starts cooling as normal.


    cant see to figure out whats causing it. I have a feeling there is a blockage in the pipe, I just wanted to see if anyone thought the same.



    any ideas are welcome.

    thanks in advance

    Rav



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Arneg Chiller cools after witched off overnight

    If there was a blocked pipe, it wouldn't cool as normal in the next morning

    I would check the control circuit, sounds like a relay not function.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Arneg Chiller cools after witched off overnight

    relay getting warm on digistat, once cools operates- whenu next goto it and it aint cooling- tap the controller with the head of a screwdriver to see if cooling starts

  4. #4
    Join Date
    Mar 2012
    Location
    uk
    Age
    38
    Posts
    4
    Rep Power
    0

    Re: Arneg Chiller cools after witched off overnight

    thank you for your reply.

    i shall check.

    much appreciated.


    Regards

    Rav

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Arneg Chiller cools after witched off overnight

    And check the compressor as it may be shutting down on klixon and resetting once it had cooled down overnight.