    Low side, high side and suprheat too high



    Hi!
    Two days ago, i have detected a gas leak on a r12 domestic refrigerator, the leak was on the pipe that goes around the door rubber of the freezer.
    So... cut out that pipe and add a new one around the condenser with same diameter and more or less same length... so far so good, i guess...
    Then... vacuum and charge it... whith R437a... I ended with low side to high (0,8 bar/ -19ºc ); high side too high (60ºc mesured with a thermometer on the middle of condenser) and the superheat was very high too.

    What to do to get the correct pressures?
    Add more pipe to the condenser ?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Low side, high side and suprheat too high

    did you change the drier? vac with a torr gauge? deburr the ends of the pipe?

  3. #3
    Join Date
    Aug 2013
    Location
    Portugal
    Posts
    20
    Rep Power
    0

    Re: Low side, high side and suprheat too high

    yes to all, i used a SMAN3... vacuum until 250u....If there was any obstruction, the high side will be high but the low will be low, right?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low side, high side and suprheat too high

    What is temperature inside?

    Probably overcharged! Don't look at superheat until temperature inside is near designed.
    Last edited by nike123; 27-10-2013 at 07:04 PM.

  5. #5
    Join Date
    Aug 2013
    Location
    Portugal
    Posts
    20
    Rep Power
    0

    Re: Low side, high side and suprheat too high

    in the inside there is -15ºc, compressor never stops, the evaporator frozed just until half ...tomorrow I will go make vacuum and charge it again with less refrigerant, adding later more if necessary .....lets see what happens...

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Low side, high side and suprheat too high

    check tev is set correctly
    also check the gauze isnt clogged
    Last edited by install monkey; 27-10-2013 at 09:04 PM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low side, high side and suprheat too high

    I don't think it is txv system. Therefore overcharge raising high and low pressure.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Low side, high side and suprheat too high

    oops just reread the original post, domestic refrigerator originally on r12 recharged with isceon 49- suitable for r12 replacement - medium temp applications- wheres the -15c coming from?? - stat welded??

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low side, high side and suprheat too high

    I would say wrong terminology. Domestic fridge-freezer and -15°C is in freezer compartment.

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Low side, high side and suprheat too high

    Cap tube systems are finicky when you change to a blend, they will only work right if the pt relationship is the same as the old refrigerant, the viscosity of the liquid, the ratio liquid to vapour, and mass flow rates etc are similar.
    Mostly found in Oxfordshire, UK :)

  11. #11
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Low side, high side and suprheat too high

    Hi Terrenas
    Did you charge as a liquid?
    Paul
    Born to fish, forced to work

  12. #12
    Join Date
    Aug 2013
    Location
    Portugal
    Posts
    20
    Rep Power
    0

    Re: Low side, high side and suprheat too high

    ok... today i did a new vacuum and a new charge, ended with same weight of refrigerant that is indicate for r12 on the nameplate, now runs perfect!!!
    Not understand what went wrong the first time...

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low side, high side and suprheat too high

    1. Overcharge
    2. Fractionation (charge from gas side)
    3. Noncondensables


    Pick one, or maybe 2 or all!
    Last edited by nike123; 29-10-2013 at 09:32 AM.

  14. #14
    Join Date
    Aug 2013
    Location
    Portugal
    Posts
    20
    Rep Power
    0

    Re: Low side, high side and suprheat too high

    Something went wrong, that's for sure...
    In my understanding, if it was overcharged, the superheat should be low... right?
    It was charged in liquid...
    Maybe noncondensables cause that problem...

  15. #15
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Low side, high side and suprheat too high

    An over charge on a warm cabinet using a cap tube will give a high suction pressure along with high superheat and high discharge pressure and temperature. Heat in the evaporator is being removed slowly so it takes some time for a critical charge system to pull down the temperature and your superheat to stabilize.

    Hmmm...looking back over the comments, Nike123 has already summed this up on post #4.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.