    Effect of oversized liquid line



    Hi everyone,
    I have recently taken over a refrigeration dept. of a small display case mfr. Among the many things I'm trying to improve I found us using 3/8" liquid line on a closely coupled 1/3 hp. condensing unit on which the reciever connection is 1/4". I was told it's because the conection size of the TXV we stock is 3/8". Silly reason,,, My question; what ill effects, if any, using a slightly larger liquid line. Thanks to all, Kengineering



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Effect of oversized liquid line

    How long is the line?

  3. #3
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Effect of oversized liquid line

    Liquid line is less than six feet from reciever outlet to TXV.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Effect of oversized liquid line

    what size is the tev inlet?- if 3/8 then maybe theyve kept it simple, i know flica do tev's suitable for 1/4 lines

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Effect of oversized liquid line

    as long as the txv are not starved - no issue
    If the World did not Suck, We would all fall off !

  6. #6
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Effect of oversized liquid line

    Ken Engineering,

    Attached is a link to a recent forum post where you asked this exact question. It was answered in detail then and should help you now.

    http://www.refrigeration-engineer.co...id-line-sizing

  7. #7
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Effect of oversized liquid line

    Wow! 8 years ago. I guess I've got a case of CRS.. Thanks for helping me revisit the topic, was a good read.

  8. #8
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Effect of oversized liquid line

    An interesting thread including the old one.

    And lets not forget that with a vrv the diameter of the main line set will be emphasized once again with the total load of both the condensor and air handlers. And again with the heat pump capability regarding both liquid and suction.
    Training may be finished but experience is never complete.

  9. #9
    Join Date
    Nov 2013
    Location
    Canada
    Posts
    10
    Rep Power
    0

    Re: Effect of oversized liquid line

    Check the pump and air filter fan capacity before turn on.On other way check your power supply connection,if there is high then it is another cause of oversized it.

  10. #10
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    Re: Effect of oversized liquid line

    Liquid refrigerant is a good solvent, so you would have to be very unreasonable with oversizing the liquid line before you get problems.