    Externally equalised expansion valve



    Morning,

    A very simple question!

    I have a gas fired 'Reznor' AHU with a retro fit cooling battery which has four stages of cooling.

    The four stages are Airedale condensers - twin condenser fan, single Copeland compressors.

    Each stage has obviously an expansion valve.

    The valves are Danfoss externally equalised TE5's with a number 3 orifice.

    Question is - when pressure testing with OFN, would you expect to see a slight pressure drop between high pressure side and low pressure side of the system?

    When gauges are closed off I have 150psi (10.34 Bar) HP side then 100psi (6.89 Bar) LP side

    Many thanks



  2. #2
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Externally equalised expansion valve

    Daz man,

    Are you applying pressure from both high and low sides of system? If you increase low side pressure does high side rise? If so is it a constant 50psi diff? are there any other valves in circuit? Regulator valves?

    I have never seen this with just an expansion valve.

  3. #3
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Externally equalised expansion valve

    The pressure should equalize across the system over time as long as you don't have a check valve holding you up. Recommend that you pressure test from high side to low side, following system flow in order to see flow through the metering device.

    "The maximum test pressure to be used should be the maximum allowable pressure, which should be stated on the equipment label. On smaller systems the suction and discharge pressures will be the same, however on larger equipment the maximum allowable suction pressure will be lower and the system will need to be tested in several sections." See attached PDF for source info
    Attached Files Attached Files

  4. #4
    Join Date
    May 2008
    Location
    Newcastle under Lyme
    Posts
    112
    Rep Power
    17

    Re: Externally equalised expansion valve

    Appreciate the response men.

    no there are no check valves in the system. I'm applying the ofn pressure down the correct flow that the gas would travel, down the liquid line.

    when I apply the ofn pressure down the liquid line the suction gauge does increase, so the ofn is coming back up the suction line.

    i am back on site today so will check to see if it has equalised out.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Externally equalised expansion valve

    Check your gauges, also!