Results 1 to 2 of 2
    Oct 2013
    Australia
    4
    Kw cooling to Kw/h power
    Hi all
    Is there a formula or estimate to calculate kw cooling to Kw used
    Just checking that there is enough capacity for the required cooling for the job
    The job is a show room that needs around 100kw of cooling
    Any help would be great
    Oct 2001
    Nottingham UK
    5,668
    Re: Kw cooling to Kw/h power
    What you are describing is the Co-efficient of Performance. Energy In v Useful Energy Out.
    This is an indication of how efficient your equipment is, not an indication of how much cooling you have or need.
    Any estimate is just that...an estimate. What you need is to calculate the total heat load you have and then compare this to the amount of cooling your equipment is rated for, to see if you have sufficient.
    Anything else is just guessing.