    Which device protects the defrost heater from overheatinf?
    Where should ohms be taken to check defrost contacts what terminals? I was thinking 3 aND 4 defrost.jpg



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Diagram help

    defrost1.jpg


    Defrost thermal protection is in series with the heater
    and the defrost contacts are 1 & 2 for the switch neutral
    for continuity.


    Rob

    .
    Last edited by Rob White; 21-10-2013 at 05:21 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Diagram help

    Quote Originally Posted by Rob White View Post
    defrost1.jpg


    Defrost thermal protection is in series with the heater
    and the defrost contacts are 1 & 2 for the switch neutral
    for continuity.


    Rob

    .
    Also which control contacts would you say would close and make the timer motor begin when the pressure in the frezzer temp control cap tube rises? would that be 1 and 2 as well

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Diagram help

    Freezer thermostat powers up the defrost timer motor.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  5. #5
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Diagram help

    Quote Originally Posted by mikeref View Post
    Freezer thermostat powers up the defrost timer motor.
    Looking at rthe diagram there is 1 and 2 ,1 and 3 1 and 4 and 2 and 4 . I was saying would 1 and 4 close? and the timer on the motor starts to run
    Last edited by bwd111; 22-10-2013 at 04:15 PM.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Diagram help

    There two circuits, compressor run and defrost switched by the timer motor. Common leg is line 1. So when the timer is a closed circuit between 1 and 4, it is on your cooling cycle, 1 and 2 (As currently shown in drawing) is defrost. If the thermostat is open circuit, no power is available for either cycles and therefore no power to timer motor.
    NB: Many timer motors were wired to run 24/7. This one isn't.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Diagram help

    Quote Originally Posted by mikeref View Post
    There two circuits, compressor run and defrost switched by the timer motor. Common leg is line 1. So when the timer is a closed circuit between 1 and 4, it is on your cooling cycle, 1 and 2 (As currently shown in drawing) is defrost. If the thermostat is open circuit, no power is available for either cycles and therefore no power to timer motor.
    NB: Many timer motors were wired to run 24/7. This one isn't.
    So after looking at diagram looks like 1 and 3 powers the timer motor

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Diagram help

    Quote Originally Posted by bwd111 View Post
    So after looking at diagram looks like 1 and 3 powers the timer motor
    Yes.............

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..