    hi all,
    \i got sabroe 163 amonia compressor ,seeing the sight glass of oil seperator i see foams on oil what might be the cause&how i cure it.
    another problem is the capacity pointer it regulates madely upper and lower by it self
    thanks in advance



  2. #2
    Join Date
    Dec 2012
    Location
    egypt
    Age
    34
    Posts
    15
    Rep Power
    0

    Re: oil foaming&capacity regulation

    ???????????

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: oil foaming&capacity regulation

    MO3TAZ,
    Maybe liquid ammonia entering suction line.
    CAn you advise us on oil & discharge temperature.
    Also what type of oil cooling water, thermosyphon or liquid injection.

    Slide valve continually loading or unloading check it is high motor amps or high discharge pressure forcing it to unload.
    If solenoid a not being energized either leaking loader solenoid or
    unload piston damaged or scored unload cylinder.

  4. #4
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: oil foaming&capacity regulation

    Hi MO3TAZ
    To add to Rangers questions regarding the foaming oil.
    Is there only one compressor?
    Is the foam there all the time?
    regarding the loading / unloading problem.
    How long has it been since the compressor was overhauled?
    Regards
    Paul
    Born to fish, forced to work

  5. #5
    Join Date
    Dec 2012
    Location
    egypt
    Age
    34
    Posts
    15
    Rep Power
    0

    Re: oil foaming&capacity regulation

    Quote Originally Posted by ranger1 View Post
    mo3taz,
    maybe liquid ammonia entering suction line.
    Can you advise us on oil & discharge temperature.
    Also what type of oil cooling water, thermosyphon or liquid injection.

    Slide valve continually loading or unloading check it is high motor amps or high discharge pressure forcing it to unload.
    If solenoid a not being energized either leaking loader solenoid or
    unload piston damaged or scored unload cylinder.
    no liquid in suction line but head is cooled by liquid injection & oil is cooled by liquid amonia from receiver
    discharge is normally 10-11 bar &oil temp from 54 to 68 degree
    motor amper is normal
    compressor loads and unloads normally by indicator is not stable

  6. #6
    Join Date
    Dec 2012
    Location
    egypt
    Age
    34
    Posts
    15
    Rep Power
    0

    Re: oil foaming&capacity regulation

    Quote Originally Posted by paulz View Post
    hi mo3taz
    to add to rangers questions regarding the foaming oil.
    Is there only one compressor?
    Is the foam there all the time?
    Regarding the loading / unloading problem.
    How long has it been since the compressor was overhauled?
    Regards
    paul
    we got 3 compressors working in parallel
    oil foaming occurs all the time only on this compressor
    it was overhaules 2 years ago

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: oil foaming&capacity regulation

    Quote Originally Posted by MO3TAZ View Post
    no liquid in suction line but head is cooled by liquid injection & oil is cooled by liquid amonia from receiver
    discharge is normally 10-11 bar &oil temp from 54 to 68 degree
    motor amper is normal
    compressor loads and unloads normally by indicator is not stable

    Can an you explain more on liquid injection, as you state you have thermosyphon oil cooling.

    Sometimes if oil cooler is to small or not working to design, people add liquid injection, so wonder if this is the case?

    Is oil & discharge temperature the same, can you also give us this temperature!

    There are usually 2 solenoids to load & unload compressor.
    There is also needle valves that control speed of loading/unloading. if you isolate them (taking note of how many turns open) then see if load position stay stable. If it does solenoids may be leaking, if it still moves by itself then unload cylinder may be scored or piston seal is damaged, or both.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: oil foaming&capacity regulation

    MO3YAZ, Also 1 solenoid is normally open the other normally closed for capacity control.
    Solenoid, I think on left when looking at end of machine, should be energized & the one on right de-energized for no loading/unloading to occur.
    Normally open solenoid has groove on armature tube under solenoid coil, this has to be energized to close.
    If coil is defective, it will unload all the time, just need to check to eliminate it.